What is the main difference between 1747-SN and 1747-BSN modules in AB.
siva_maddala
Apr 2006
BOMBAY
63
hello sir
welcome to the automation world. What is the main difference between 1747-SN and 1747-BSN modules in AB.If any one knows pleaae give reply.
thanks and regards
siva
The SN is a remote I/O scanner (SN). The BSN is a remote I/O backup scanner (BSN). Basically, if you are using redundant Slc 5/0X processors, the BSN allows the same functions of the SN but allows you to connect a second processor on the RIO link and have a failover situation.
Note that the BSN will only backup the remote I/O. 2 chassis each with a processor, and a BSN module. These are connected to remote I/O (a least one chassis with an ASB module and your I/O. They are also connected to each other via the HSSL connection on the front (high speed serail link) for failover communications.
Make sense?
Marc
I want to know what is the main difference between PLC and DCS.if PLC Perform every task why we use DCS.Plesae can some one tell me about DCS5000...
17
27,368
188
Hello Everyone- I'm working on a new network deployment of AssetCentre and I am not able to authenticate with the application using our...
404
TLDR: I try to establish the OPC communication between Kepware OPC DA Client to ABB 800xA OPC DA Server. In the Kepware OPC quick client of poll...
854
Main rack contained power supply 140cps52400 and 140cpu43412A and RIO HEAD 140CRP93100 in addition to another I/o cards . Another remote rack...
1,866