timer for scan time

i am using a micro logic 1500 ab plc i would like to setup a timer or counter to check scan time for the plc i am not sure that i trust s:35

jim cav
  Reply With Quote
Old October 31st, 2008, 09:38 AM   #2
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 6,274
Set up a bit that alternates between on and off each scan. Then set up another bit to latch on upon command from you. Use the alternating bit to increment a counter with a preset of 500. Use the counter's DN bit to reset the latch. While the latch is true, enable a retentive timer. When the latch turns off, the timer's ACC value is the time for 1000 program scans. Divide by 1000 to get the average time for the 1000 scans.
  Reply With Quote
Old October 31st, 2008, 09:41 AM   #3
OZEE
Member
United States

OZEE is offline
 
Join Date: Mar 2006
Location: Kansas
Posts: 1,695
1) Why are you interested? (In 20 years of doing this, I've never seen scan time be an issue...)

2) Why don't you trust S:35?
  Reply With Quote
Old October 31st, 2008, 10:32 AM   #4
Brijm
Lifetime Supporting Member
United States

Brijm is offline
 
Brijm's Avatar
 
Join Date: May 2006
Location: St. Marys, PA
Posts: 640
Quote:
Originally Posted by OZEE
1) Why are you interested? (In 20 years of doing this, I've never seen scan time be an issue...)

2) Why don't you trust S:35?
I had an older tech the one time, insist, that the scan time status bit was inaccurate on AB... This guy was very smart, but was also known to bend the truth a little, to make others look bad. I checked the scan time status, but he insisted that this was the problem (not his programmin of course). I was young at the time, and wanted to see for myself, as well as starting to catch on to how this guy operated.

So I set up a solid state output to toggle each scan, and put an oscilloscope on that output.... Turns out, that the status word matched the ocsilloscope exactly every time... The guy still said, that I was wrong, but the boss didn't seem to give it as much credit.

-MUR
  Reply With Quote
Old November 1st, 2008, 11:21 AM   #5
CeCo3
Member
United States

CeCo3 is offline
 
Join Date: Nov 2006
Location: Northern California
Posts: 52
I too connected an output to toggle once per scan, but instead of an oscilloscope, I connected a data acquisition instrument to it. (the advantage is I can review what I recorded.)

Anyhow, the scan time matched the S? bit (SLC5/04), but I discovered something interesting in the process. The scan rate was steady at 4msec, rock solid. However, when I went online with RSLogix500, every tenth scan or so would be 11msec. I attributed this to the the frequency at which RSLogix was being updating over the comm port.

For my application this was found to be a problem as it introduced variation into the load cell measurement being performed once per 50msec.

Congrats on using the oscope. It seems so few do. You've provided some degree of proof. Data driven decision making; your boss should have given you more credit, even on the side.

CeCo3
  Reply With Quote
Old November 2nd, 2008, 09:38 AM   #6
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: barranquilla
Posts: 2,481
Quote:
Originally Posted by CeCo3
For my application this was found to be a problem as it introduced variation into the load cell measurement being performed once per 50msec. CeCo3
Just to satisfy my curiosity, what is your applicaion so fast that you need 50 mS as an update time.
__________________
My two cents.
  Reply With Quote
Old November 2nd, 2008, 04:07 PM   #7
CeCo3
Member
United States

CeCo3 is offline
 
Join Date: Nov 2006
Location: Northern California
Posts: 52
One of my clients manufactures tablets using bi-layer rotary tablet presses similar to the ones pictured here:

http://www.aaronequipment.com/FullSi.../520594a.photo
http://www.aaronequipment.com/FullSi...s/86932a.photo

The presses spit out finished tablets at a rate of more than 1,150/minute (1/(1150/60)=52.2msec). A load cell at each layer measures the amount of registered force when the granulation if compressed a fixed amount. Precise timing is needed to ensure consistent measurement is performed cycle after cycle. As I mentioned previously, when RSLogix was connected to the PLC, every tenth scan or so was delayed an additional 7msec and this caused a lower force value to be registered. It took some serious investigation to identify the cause of that problem.

Back to the original issue of the S35 time being accurate, I've never had reason to doubt the accuracy of the average scan reported in any A-B PLCs. But after what I've learned about scans, the only way your going to know for certain is to monitor the S35 bit (or equivalent) by tieing it to an output channel and monitoring it with some sort of recording instrument.

There are other things to consider as well, such as event-based subroutines that do not execute every scan.

I hope this answered your question.

CeCo3
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 5/05 Scan Time vs Input Pulse robertmee LIVE PLC Questions And Answers 11 May 20th, 2008 10:54 PM
A plea for help...and mentor damianjones LIVE PLC Questions And Answers 72 February 7th, 2007 11:10 AM
Timer sequences allan4169 LIVE PLC Questions And Answers 20 July 7th, 2006 10:13 AM
[S5-155U CPU948]about cycle time ? apple LIVE PLC Questions And Answers 2 June 30th, 2006 01:32 PM
difference between S7-300 and S7-200 timer Pandiani LIVE PLC Questions And Answers 8 April 27th, 2005 07:13 AM


All times are GMT -5. The time now is 10:05 PM.


.