Hello, first of all, I want to say thanks to everyone who is seeing this post.
I have a problem with an SLC 500 5/05 processor. I need to download a program, you guys know that this processor has two channels:
- Channel 0 is for RS-232 Serial Communication.
- Channel 1 is for Ethernet Communication
I'm trying to communicate through RS-232 channel but my RSLINX doesn't see the processor. I click "Auto-Configure" with the Com port selected, but it only says "Unable to verify settings due to packet timeout. Check all cables and configuration and try again"
The driver for the USB RS-232 converter it's working properly, I used the cable to communicate with other PLC and it works.
I also tried to do the ethernet communication assigning an IP to the processor but I can't use the tool BOOTP because the MAC Address doesn't appear.

In the CPU Module, the FAULT led is blinking. I know this means that the processor isn't configurated or doesn't have a program in it.

I don't know what else to do, please help me if you know another way to assign an IP Address.....
 
Channel 0 could be set for DH-485 comm's, or for ASCII comm's if needed by another device. It can also be disabled completely.

To try the DH-485 option use a 1747-UIC to the DB-9, with a null-modem cable.

The best option would be to download and install WireShark. a free network monitor. With this you should see the 5/05 give its IP address, or it may be requesting one from a BOOTP server. If there is an HMI attached that would probably look at a specific IP address so the PLC should have a set address.

EDIT: if you have the porgram ready to download you could reset the 5/05 by pulling the battery and shorting the VB terminal to ground for 20 seconds. Then the PLC will default to DF-1 - either at 1200 or 19200 baud depending on the firmware revision in it.
 
Last edited:
Some USB converters just plain won't work with the SLC500, even though they will work for other PLCs. I have used a Keyspan usa-19hs with success with this processor. Google it for sources.
 
A lot of inexpensive USB/RS232 converters can't rapidly change framing or speed settings, which is necessary for the "Autoconfigure" feature to work correctly.

The settings are pretty straightforward to just set correctly for the DF1 Full Duplex defaults on the SLC-5/05.

19200 baud 8/N/1 framing
CRC error checking
DF1 Full Duplex
SLC/MicroLogix/PanelView device type

You can also use Wireshark to "sniff" the IP address of the SLC-5/05, especially if you can connect directly to it from your computer and look for ARP packets.
 
I also tried to do the ethernet communication assigning an IP to the processor but I can't use the tool BOOTP because the MAC Address doesn't appear.

....

I don't know what else to do, please help me if you know another way to assign an IP Address.....

You need to reset the PLC to factory default then use Bootp and the mac will show up, since the light is blinking you lost your program anyways so just reset it and then you will be fine, you can use controlflash to load the IP, its a little easier and faster
 

Similar Topics

I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
Replies
3
Views
524
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
Replies
7
Views
3,016
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
Replies
9
Views
1,801
I recently inherited some 5/04 CPUs and a single 5/02 CPU that I need to pull the programs from. The 5/04 CPUs didn't pose any problems. I...
Replies
14
Views
3,051
Good Morning , How do you replace the battery on a SLC 500 CPU without loosing the program , since you need to remove the CPU , and the...
Replies
11
Views
12,056
Back
Top Bottom