communicate with slc 5/04
beardog
Nov 2012
tampa
I have a SLC 5/04 PLC and CP3 cable and DF1 selected in RSlinx, when I do auto-configure it says failed to find baud and parity! check all cables and switch settings! I have baud set to 19200, parity none, stop bits 1, station number 00, error checking crc, protocol full duplex, also the battery light is on and DH+. I want to download the program before I change the battery but I cannot see the processor. I have two cp3 cables so I am sure they are not both bad. I also have 1747-UIC cable for USB and still can't see processor.
With some types of USB to serial converters, autoconfigure may not work consistently. Are you using a real serial port or a converter?
That all looks fine for a typical DF1 connection.
I would think that you would want to Upload (to your PC) the program before changing the battery, just as insurance...even with no battery the SLC can hold its program in memory for at least 30 minutes...I have seen the onboard cap in a new processor hold the program over night with no battery installed. There are other things that could go wrong and wipe out the program, so I think getting a fresh copy up front is still a wise move.
With a/b stuff, download, means send a program to the processor and overwrite whatever it contains. Be careful with these terms.
The 1747-UIC is used for DH485 connections, not DF1.
The SLC serial port can be set up several different ways. it might be set for DF1, DH485, or User (ASCII) mode.
I would suggest (if using a USB to RS232 converter) that you try manually changing the baud rate and hitting OK, then open a RSWho window after each adjustment and look for it to appear under your DF1 driver. Give it a few seconds to appear. Also, turning off autobrowse and using the Refresh button to manually force the driver to browse is sometimes helpful.
Sorry I meant upload and used cp3 for df1 and my uic driver for uic converter, I have tried both ways, neither seem to work when I do RSwho I will have to try your suggestion and manually change baud
... used cp3 for df1 and my uic driver for uic converter, I have tried both ways, neither seem to work when I do RSwho I will have to try your suggestion and manually change baud
I don't understand what you mean by both ways. You tried the UIC with the CP3 cable (which would only work if the SLC serial port is set up for DH485...much less common than DF1).
What is the 2nd way that you tried?
The RS232 port may be configured for DH485. With nothing plugged into the port, watch the RS232 light. Does it stay out or does it flash once in a while?
uic with uic driver and cp3 cable with df1 driver. two different drivers
The UIC device will only communicate with the SLC if its serial port is set up for DH485.
This is likely your problem.
If (likely) the SLC serial port is configured for DF1, you need a serial port, or USB to serial converter and the DF1 driver (and the CP3 cable).
I am trying to connect to a machine in my facility for troubleshooting, but I can't make it work. I am using a 1761-clb-pm02 from allen bradley...
18
3,172
Hello, first of all, I want to say thanks to everyone who is seeing this post. I have a problem with an SLC 500 5/05 processor. I need to download...
2,796
Hello. I'm trying to communicate a DOP-B07E515 HMI(DAKOL) with a SLC 5/03 PLC. The serial port connection rs232. I am using a cable with the...
1,042
Hi everyone, I have an AB 1747-L20B PLC that has a CPU fault, I am trying to connect to it with RSLogix 500 Pro to see what the fault is and to...
3,296
Dear Friends, We have a setting machine in which 20 Parker Servo Drives and motors (name plate images attached) used to place the tools at...
3,878