Panelview standard 1000 error 436

clank

Member
Join Date
Jan 2005
Location
Ontario
Posts
46
Hi All

We have a Panelview 1000 that has only 2 pages. A main page and a manual page. At times when go to page is touched, the screen comes up.... Error 436 Remote Device has screen control and it does take some time before this error stops displaying. I realize it is something in SLC 5/04 or is it something in apllication....but what?? We do not want a remote device to have control. I am hoping you guys could point me in right direction...this problem is a pain in the butt
Thanks
 
Check your control tag section in panelview 32 programming software.
If you see something, deleted and re-download.
I had this problem couple of times too. Good Luck
 
More info on what Doylen said. Altough I would not call it a problem, its a very useful feature. But as Doylen said if you don't want it then delete it.

screenselect.JPG
 

Attachments

  • ControlTags.pdf
    53.5 KB · Views: 127
Last edited:

Similar Topics

Hi, I have a retrofit enhancement on an existing PV1000 (Not PV +). It is a 2711-T10C10 with a RS232 port and DeviceNET. I need to send a string...
Replies
2
Views
2,845
I have a Panelview 1000 (series a) that has a blank screen. I swapped the screen with a spare PV and it worked. I need to upload the program to my...
Replies
6
Views
7,037
Had an interesting experience this morning. An old Panelview 600, 2711-K6C5X series B to be precise, comes up as error 32. Unfortunately it...
Replies
0
Views
207
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
Replies
3
Views
636
Good evening. I am trying to get a SLC 5/03 connected to a Panelview Plus 7 Standard using a Moxa Mgate EIP3170 and I am not having much luck. I...
Replies
2
Views
517
Back
Top Bottom