Panelview Standard RTC and firmware…

plvlce

Lifetime Supporting Member
Join Date
May 2017
Location
Michigan
Posts
1,074
Had an interesting experience this morning.

An old Panelview 600, 2711-K6C5X series B to be precise, comes up as error 32. Unfortunately it seems we don't have a spare, but this thread seems to suggest that replacing the RTC will do the trick, and I know I've got a couple PV 1000s on the shelf.

Sure enough, one of them is a series B that uses the same DS1643-C03 chip, so I pop it out of that one and into the 600… and the panel stalls at self test 24 -- 'Performed CRC base firmware check'.

Not sure what the firmware would have to do with the RTC, but I know how to handle that -- I grab a flash card, copy the appropriate firmware on, and drop it in. The firmware copies to the terminal… and now it's error 26, 'Firmware not compatible with hardware'. I'm confident I got the right firmware for the terminal (I double check anyways though; I did).

As I'm scratching my head over this, production comes over and asks if I can for the time being I can go online with it and toggle it into auto -- during normal operation they don't use the HMI much, it's only when something goes wrong that it's really needed. So for the moment I swap the original RTC chip back in, close everything up, and then power on… and it boots up to the config page. I drop the program back in and it runs, no further related issues.

But I've still got a couple questions left unanswered. Why did a same model RTC chip yield a firmware compatibility error? Is the original RTC chip going bad and pulling it out and plugging it in again breathed a little life back into it? Or was the original error 32 a red herring and somehow the firmware flash I did while I had the other one in what actually fixed the problem?

All I can say for sure is that this HMI just moved to the top of my 'convince management to spend the money on an upgrade' list.
 

Similar Topics

Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
Replies
3
Views
639
Good evening. I am trying to get a SLC 5/03 connected to a Panelview Plus 7 Standard using a Moxa Mgate EIP3170 and I am not having much luck. I...
Replies
2
Views
521
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
Replies
1
Views
672
Hello All. I have an interesting one for you. I have a brand new Panelview 600 Standard 2711-K6C20 and I'd like to get it to talk to an L81E...
Replies
7
Views
2,013
I have a failing Panelview connected to a SLC 5/04 over DH-485 using a pair of SLC 500 Link couplers as the PLC and HMI are about 125 feet apart...
Replies
7
Views
2,406
Back
Top Bottom