4 wire proximity sensor to plc input
Hi. I'm trying to teach myself PLC's on a mitsubishi FX2N-16MR.
I have connected a 4 wire PNP proximity sensor as NO to my plc but it is not switching the output. The indicator on the sensor shows that its working when it detects and i have connected the NO wire to my input and the NC wire to my 0V as per a wiring diagram i have. My program simply has 1 NC input and 1 NO input connected to a respective output. I feel that maybe i have not specified something in GX developer? I am using a CQ35-25NPP-KC1 sensor. Thankyou for your help, please excuse my naivety. |
|
|
|
#2 |
|
Member
![]() Join Date: Jan 2007
Location: Michigan
Posts: 1,059
|
I would not attach the white wire to 0V. While sometimes the white wire is not used, it can be used as a NC output, or sometimes 0-10V or 4-20ma output, etc. Keep the wire taped off and not terminated on any terminal. What happens if you manually switch voltage to the input (using a jumper wire from 24V)?
|
|
|
|
#3 |
|
Member
![]() Join Date: Dec 2008
Location: Izmir
Posts: 43
|
|
|
|
|
#4 |
|
Member
![]() Join Date: Mar 2011
Location: Qld
Posts: 4
|
Thanks for the response guys.
I have tried with the NC wire removed, and manualy switching on the input did not work either. Also, i can see when in monitor mode that the X1 input is not being activated. |
|
|
|
#5 |
|
Member
![]() Join Date: Jan 2007
Location: Michigan
Posts: 1,059
|
Does the indicator for the PLC input turn on?
|
|
|
|
#6 |
|
Member
![]() Join Date: Mar 2011
Location: Qld
Posts: 4
|
It doesnt.
Is there anything else i need to do to associate the sensor with the ladder program in Gx Developer? |
|
|
|
#7 |
|
Member
![]() Join Date: Jan 2007
Location: Michigan
Posts: 1,059
|
You shouldn't. And I believe the PLC Input indicator should turn on regardless of whether or not it's addressed in the PLC program.
Do you have access to a voltmeter? Can you make sure that 24V is being supplied to the Input terminal? Your picture shows the RUN indicator on the PLC is off. Is that just because the PLC is powered down when you took the picture? |
|
|
|
#8 |
|
Member
|
For PNP sensors you need to make sure the S/S terminal is connected to the 0V terminal
|
|
|
|
#9 |
|
Member
![]() Join Date: Jan 2007
Location: Michigan
Posts: 1,059
|
|
|
|
|
#10 |
|
Member
![]() Join Date: Mar 2011
Location: Qld
Posts: 4
|
Thanks for your help guys, i should of realised this. Hopefully i will have a more complex problem next time..
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| LG PLC, do I use PNP or NPN proximity switch for input | Peter LG | LIVE PLC Questions And Answers | 4 | September 20th, 2009 08:59 AM |
| AD DL06 programming help | ThermoT | LIVE PLC Questions And Answers | 46 | June 7th, 2006 08:21 AM |
| PLC input voltages | ronbol | LIVE PLC Questions And Answers | 2 | February 13th, 2006 04:15 PM |
| Pull-up resistor & PLC input????? | Charles1 | LIVE PLC Questions And Answers | 6 | January 27th, 2006 01:48 AM |
| Thumbwheel Switch Input /S7-200 PLC | Tomy | LIVE PLC Questions And Answers | 2 | April 8th, 2004 06:17 PM |