plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old May 4th, 2011, 09:26 PM   #1
iahi_2005@yahoo.com
United States
iahi_2005@yahoo.com is offline
Question 4-20 Loop 2 Wire vs 3 Wire
Guys,
I am really confused about 4-20 ma current loop 2 wire vs 3 wire...what is the difference?
Does the difference have anything to do with the sensor being powered separately or in loop?
In My case the sensor is a Gas detector and sends output to PLC Analog Input.So is the sensor being powered from the PLC Analog Input Card?
Thanks..i would really appreciate it if you could clear that up...
Old May 4th, 2011, 10:28 PM   #2
Mickey
United States
Mickey is offline
Mickey's Avatar
A picture is worth a thousand words. (or something like that )
Give us the exact part number of your gas sensor or a link to it's manual.
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old May 4th, 2011, 11:59 PM   #3
labeledas
Canada
labeledas is offline
labeledas's Avatar
if it is resistance based it is probably used for compensation, simialr to an rtd
Old May 5th, 2011, 12:45 AM   #4
Vic
Canada
Vic is offline
huh?
Old May 5th, 2011, 08:13 AM   #5
Tom Jenkins
United States
Tom Jenkins is offline
Tom Jenkins's Avatar
Quote:
Originally Posted by iahi_2005@yahoo.com View Post
Guys,
You are correct! Two wire loop powered sensors are usually simple devices like pressure or temperature transmitters that don't need much power. They use a diode or resistor to create a voltage drop inside the device to power the circuits.
Three and four wire devices are more complex transmiters that need more power than can be easily taken from the loop. Your gas detector is probably three or four wire, but the manufacturer's manual should identify the wiring.
Mickey's post shows the wiring difference perfectly.
Old May 5th, 2011, 08:38 AM   #6
iahi_2005@yahoo.com
United States
On your picture, is the power supply the analog input card?...or can the analog input card never be a power supply also?
Old May 5th, 2011, 09:12 AM   #7
Mickey
United States
Mickey is offline
Mickey's Avatar
That would depend on the card your are using. But most that I am familiar with use a separate power supply.
What analog input card do you have ( complete catalog number)?
__________________
Mickey
Old May 5th, 2011, 10:44 AM   #8
iahi_2005@yahoo.com
United States
I am using a 1756-IF16 Card (Allen Bradley)
Old May 5th, 2011, 11:07 AM   #9
Mickey
United States
Mickey is offline
Mickey's Avatar
The card does not supply the power. You will need an external power supply.
__________________
Mickey
Old May 5th, 2011, 02:40 PM   #10
inst_tech
United Kingdom
inst_tech is offline
On the platform i work on all the line of sight and point gas detectors supply 4-20mA to the fire and gas cards ie. they have their own power supply. The catalytic gas detectors are powered from the fire and gas cards and work on resistance.
Old May 5th, 2011, 02:51 PM   #11
I is a noob
United States
I is a noob is offline
I is a noob's Avatar
i have some gas monitiors that are two wire 4-20. Google OI-675. Various gas set ups, are Class 1,Div 1 and work from on 12 & 24 VDC systems. Easy as pie but are in the 1.7k range.....
Old May 5th, 2011, 02:55 PM   #12
albertabound
Canada
albertabound is offline
http://www.bapihvac.com/content/uplo...igurations.pdf
Old May 5th, 2011, 10:03 PM   #13
iahi_2005@yahoo.com
United States
Looking at the picture the only difference between the 2 wire and 3 wire is the extra ground wire...but what is the significance of that?...
Old May 5th, 2011, 10:29 PM   #14
Mickey
United States
Mickey is offline
Mickey's Avatar
Read Tom's second paragraph post #5.
Look again at the drawings. The 2 wire device is loop powered. The 3 wire device is first powered by the 24vdc power supply and has a separate output which goes to the PLC's input, it's not loop powered. The power supplies common and the PLC's minus input are tied together to complete the 3 device's output circuit.
__________________
Mickey
Old May 5th, 2011, 11:17 PM   #15
iahi_2005@yahoo.com
United States
I am sorry to keep asking..if like you say that is the case what is the difference between 3 wire and 4 wire they are both separetely powered.....when would you use one over the other
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
4 - 20 MA 4 wire to 2 Wire Conversion cbe.krishna LIVE PLC Questions And Answers 6 February 14th, 2011 09:46 AM
How many of you have used cascaded loops? Peter Nachtwey LIVE PLC Questions And Answers 51 April 27th, 2010 04:36 PM
Lost my 4-20 ma loop cirtcele LIVE PLC Questions And Answers 6 May 20th, 2009 10:51 PM
4-20ma signals shoelesscraig LIVE PLC Questions And Answers 22 April 27th, 2009 03:00 PM
Tuning Primary Loop in Cascade Loops?? RPax LIVE PLC Questions And Answers 9 November 14th, 2007 02:53 PM