Hi,
I am using GE Fanuc PLC to calculate the Flow rate in cubic meter per hour from pulses output. i.e. Pulses per second. But the method i used is suitable if i have pulses per volume defined. But for (LF Meter) through which i am measuring Flow rate, that is not defined. Hence any other methods which could give me precise flow rate value in Cubic meter per hour. |
|
|
|
#2 |
|
Lifetime Supporting Member
|
What output your meter is giving you may be helpful. Specific meter you are using even more helpful...
Best guess from what you have given, is that if you have a pulse output meter that is not indicative of a volume, then it is likely equal to a speed. If you know the speed the media is traveling, then you need to find the area of the container it is passing through. Meters Squared * Meters/sec = Cubic Meters/sec Precision will be based on how careful you are with your area calculations, and how laminar the flow is.
__________________
Brian |
|
|
|
#3 |
|
Lifetime Supporting Member
|
Take the number of pulses you get in (1 minute X 60 )X cubic meters in each pulse. If you don't know how many cubic meters per pulse you will need to calculate this first based on what you do know.
Or maybe I don't understand the question?
__________________
LEARN something today so you can TEACH something tomorrow. DETAIL in your question promotes DETAIL in my answer. Do you "Believe"? Do you vote? Please Read: Dominus Vobiscum <))>( Last edited by RussB; October 23rd, 2012 at 07:24 AM. |
|
|
|
#4 |
|
Member
![]() Join Date: Oct 2012
Location: hyderabad
Posts: 6
|
The formula i used for this calculation is - (pulses/ sec* 3600)/max no. of pulses per cubic meter. The pulse/sec output i am getting by configuring my PLC in HSC mode. The number of max. pulses per cubic meter is defined per meter. The meter i am using for this operation is Romet Meters. Basically i am performing the Proving Process. So for some meter the max. number of pulses per cubic meter is not defined. So there the Problem arises and for some LF Meters we don't even get pulses/ sec from Register. So just by using the output pulses from Meter i need to calculate the Flow rate. Hope i am quite clear with my Query. Need your inputs on this.
|
|
|
|
#5 |
|
Lifetime Supporting Member
|
If I'm understanding correctly, it sounds like two problems.
1. Scale will change based on meter used - You may need an HMI or some way to update the scale based on the meter. 2. Some Low Flow meters do not give you a pulse every second, or enough pulses to preform an accurate measurement. In this case you may need to change your time base.
__________________
Brian |
|
|
|
#6 |
|
Member
![]() Join Date: Oct 2012
Location: hyderabad
Posts: 6
|
With out changing my Time Base can i any how calculate the Flow rate. For some Low Frequency Flow meters the pulses are not so frequent so in order to have proper flow rate measurement i want to make my final calculation independent of Time Base. Can you suggest any method which will be useful for such calculations
|
|
|
|
#7 |
|
Lifetime Supporting Member + Moderator
|
It has been discussed many times before.
Do a search for "flow rate pulses".
__________________
Jesper
|
|
|
|
#8 |
|
Lifetime Supporting Member
|
Basically you either need to determine if a longer time base is suitable for all application (Perhaps measure volume over 5 sec instead of 1) or make an adaptive time base. Number of seconds vs a minimum change. With this you will also need a timeout, after which you determine there is no change, and move a 0 into your flow. also you will need to modify the 3600 in your equation based on the amount of time your sample is.
__________________
Brian |
|
|
|
#9 |
|
Member
![]() Join Date: Oct 2012
Location: hyderabad
Posts: 6
|
i have tried working out with program for calculating TD between two pulses but it is true for first 2 pulses but after that its not taking into consider pulse between 2 & 3 and same continues. it is considering pulses 1 & 2, 3 & 4, 5 & 6. But it is not considering TD between the pulses 2 & 3, 4 & 5 and so on. The flow rate value what i am getting is with gap of one Pulse? Can any one help me with this ?
Last edited by shujauddin; October 23rd, 2012 at 08:15 AM. |
|
|
|
#10 |
|
Member
![]() Join Date: Oct 2012
Location: hyderabad
Posts: 6
|
The formula used is - 3600\time difference between two pulses
|
|
|
|
#11 | |
|
Lifetime Supporting Member
|
Quote:
You mentioned using a HSC which means that you are recording total volume and calculating flow. I believe the normal means for what you are trying to do is:
__________________
Brian |
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Metering Pump control with a flow meter | VIRUZIE | LIVE PLC Questions And Answers | 8 | September 15th, 2012 07:56 PM |
| Calculate Flow Rate m3/h by digital input pulses | gespro | LIVE PLC Questions And Answers | 0 | November 5th, 2011 11:25 AM |
| How to calculate realtime kwh from a kwh meter with puls output | hapetter | LIVE PLC Questions And Answers | 7 | December 13th, 2010 07:01 AM |
| Flow Meters Scaling - Converting Parameters | ABColin | LIVE PLC Questions And Answers | 13 | January 5th, 2010 05:55 PM |
| Flow Meter Problems!!!!! | RPSTiger | LIVE PLC Questions And Answers | 16 | March 25th, 2009 03:56 PM |