1 analog voltage output to 2 inputs
tempo
Feb 2014
Tallinn
Hey guys.
Im working on a PLC project. A voltage output from VFD is connected to a PLC analog input card. I will need the same information in my PLC. The question is, can I connect a wire from that input parallel to my PLC input.
I am asking this, cause the original plc is working 24/7 and i cant take it away. Or will it cause problems in the first plc. Extra voltage drops?
Furthermore, i know that wire length isnt a problem with 4-20 mA analog output, but what about 0-10V output? I might need to send the signal over 20-50 meters.
Thanks in advance
You should be OK running them in parallel. Voltage drop isn't a problem with that distance. Just make sure that the two load resistances in parallel are above the minimum for the transmitter - that shouldn't be a problem, but it is good to check.
Pretty simple question, but I was wondering how I can set the Analog Output 1 of an S7-1200 (DC/DC/Relay) to be proportional to a data tag. I...
850
Hi; I need to monitor and log the 3phase AC input voltage for which I need a device to convert AC input voltage (say 350 - 440V) to analog (0-10v...
1,376
I'm experimenting with Automation-Direct "Terminator" I/O analog modules and wondering if anyone has experience in configuring the T1F-16DA...
4,506
Hi I am getting a cpu 314c-2dp. I need to control hydraulic servo valves that need +/- 5V for proportional speed/direction. I am looking into...
1,608
Hi all, I want to control the speed of a three phase motor through a VFD. For the input to the VFD I am using a PLC. Now at present I am using...
8,930