15 years in, and help
4) All the Photo-Eyes (PEs) supplied with the Accutrac 360 are Light Operate PEs. This means that the input to the plc is ON when the emitter is aimed at the receiver and its line of sight is clear.
Additionally, the amber indicator on the top of the receiver illuminates to indicate that it sees the beam and that they are not blocked.
Slight change of wording highlighted there...
Also, at the end, I would change directions if there are multiple sensors not working and break out the voltmeter.
I would take a voltage reading at the farthest one...If there is no voltage, then backtrack to the next junction and inspect. You will be looking for a break somewhere feeding the "dead" group. If the voltage is found to be low, start unplugging (or disconnecting) sensors and emitters one wire or cable at a time, and look for a jump in voltage. Then swap in one known good spare emitter and receiver to rule out cables or wiring. Make sure the new or proven sensor is marked so you don't mix them up (if dealing with QD cables).
To prove PLC inputs, I would teach them to use a jumper wire at the PLC while verifying that the HMI also confirms that the 'puter sees the little light you are looking at too.
Good Evening , After running for 2 years , I have a few Powerflex 525 drives faulting out with a F 73 Ethernet Fault . What have you guys...
2,623
R
I'm using a rosemount flowmeter sending an analog signal back to the PLC (of flow). How can i use this in the PLC to make a totalizer of how many...
13,090
Years ago, when I was an Automation engineer, I relied on this site heavily, for help, with questions I had. Many times, this site saved my...
173
Hello, We have had a machine running for the last 10 years. It has 2 x Kinetix 300 drives. Around a year ago, one of the drives failed. We were...
442
Some things in the past 10 years have not changed, people are still asking for password work arounds, some are asking for help with homework and...
1,038