Hello, I am kinda new to automation, I had an issue with 1743-EPAC which supply's 13 IO , when we inspected it there was a short circuit inside it, the components we're almost burned.
We had 4A CB protection on it , but it didn't work.
I have 2 questions :
1_ what could have caused the EPAC to short circuit only and the rest of components are intact
2_ we replaced the EPAC with EP24 and PFD
I read that both EPAC( convert voltage from 110 to 5V ) and EP24 ( convert voltage from 24 to 5V ) convert the voltage to backplane volt which is 5V if so why we needed the PFD ? Why couldn't we replaced the EPAC directly with EP24 since both of them convert the voltage to 5V .
Thank you .
 
Point Io has field power and module/bus power on separate rails. The leftmost module/buscoupler provides 24vdc field power and 5v bus power. After a number of modules (varies based on module power consumption) the 5v bus runs out of power and additional power injection is required (1734-EP24DC/1734-EPAC). The DC24/AC also provides a new supply for field power and can be changed between DC/AC as needed. If there is no need for additional module/bus power there can be a 1734-FPD installed the provide a new source for field power. We might have 2 or 3 FPD installed on a rack with different power supplies for different safety zones on output cards.
 
Point Io has field power and module/bus power on separate rails. The leftmost module/buscoupler provides 24vdc field power and 5v bus power. After a number of modules (varies based on module power consumption) the 5v bus runs out of power and additional power injection is required (1734-EP24DC/1734-EPAC). The DC24/AC also provides a new supply for field power and can be changed between DC/AC as needed. If there is no need for additional module/bus power there can be a 1734-FPD installed the provide a new source for field power. We might have 2 or 3 FPD installed on a rack with different power supplies for different safety zones on output cards.
What is the difference between field power and bus power, and what are the sources of theses powers
 

Similar Topics

I have AB 1734- Point I/O In this particular case, I intend on using 1734-EPAC module to power adjacent modules (to the right). The manuals...
Replies
4
Views
2,455
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
53
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
16
Views
615
I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
232
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
Replies
8
Views
349
Back
Top Bottom