1746-NO4I voltage ability?
Jan 2003
Michigan
490
Hey all. Ive been asked to use a slc NO4I current output to drive a pneumatic valve actuator. The actuator only has a 4 - 20 input on it, and draws it operating power from the current loop. It states it needs 5V to operate. Does anyone know if the NO4I output can supply this level of voltage on the output, or am I going to need to do something like wire a DC supply in series with it? Thanks
matt
Do you have a part#/manufacturer for the actuator? The load range for the NO4I is 500 Ohms. I seriously doubt the acutator uses the loop power to actually move the valve. The module will power the loop, but not the actuator itself.
OK I guess I didn't think about the application enough. I had never seen the type of actuator you are talking about but after a little research it looks like you are correct. The NO4I will use 24VDC to drive the loop.
Looks like you should be fine. The manual says "at least" 5 volts. As long as your wire run isn't rediculous (like a mile haha) it will work.
Dear Friends, Need your expert opinion. We have SLC500 and installed Analog Output module is 1746-NO4I. Scaling and PID configuration is 0~16383...
1,962
Today we started commissioning an SLC 5/04 system that a customer purchased used. The entire system presumably was fully operational at the...
3,789
Greetings; We have a flow meter measuring our Process Water flow, and it sends a 4-20 mA signal to a SLC 5/05 through a 1746-NI8. The head...
2,995
I've experiencing problems regarding the decimal equivalent to mA reading of each channel. Based on 1746 NO4I manual, the equivalents are: 1...
2,098
Hi, I'm in the field. Long story short... their original devices have failed, and they're not getting the required temperature (analog) data. I...
2,048