1747SN block xfer from old slc 5/04 to PV900
DST1
Feb 2009
Indiana
27
The problem started with an error 208 in my PV900 after a program change and download to my slc 5/04. The logic had worked for over 2 years before the change, so I downloaded the original program back into the plc but still have the same problem. The communication is ok because I can still read data from the plc in the HMI but for some reason I can't write to the plc. After tracking the numeric entries that were popping up the "208" error , I noticed that they are associated with block transfers in the plc program. I also noticed that the BTR and BTW logic seems to be "locked" up.
Is there a way to get my sequence going again? The logic is almost identical to the "bidirectional continuous block transfer example" on page 144 of the 1747SN user manual. Do I need to reconfigure my #N file and then download again? I know you have to set bit 7 of word 0 to a "1" for BTR or a "0" for BTW, but I didn't see if any other bits needed changed for the startup config.
Any help on this would be appreciated!
You can write a Kick start rung with an unlatch of the DN Control Bit. Add a TMR to trigger the bit. You do not want it to trigger during normal Operation.
Does anyone know of an AB publication for RIO BTW/BTR to the 1794IE8, The only literature I find on AB site is PLC-3 & PLC-5 I am using 1747SN, I...
13,542
Hi currently my work parther an I are working into trying to visualize a set of values on a PanelView 550 that is connected tru a RIO connection...
6,506
Hi, I am trying to get some flexi IO communicating. The scanner has its steady green light on The G file is all the default values.The first two...
5,227
J
I am having trouble with an existing SLC5/05. It was working fine but after power cycle, we lost data to all but 1 1794-IE8 module. I looked at...
3,117
In the past, we have used AB 1492 feed thru screw terminals a lot. Lead time on these with our distributor is terrible. Is there an almost...
121