I am having trouble with an existing SLC5/05. It was working fine but after power cycle, we lost data to all but 1 1794-IE8 module. I looked at the program and there's a BTR instruction for each IE8 that is has rung condition true but the EN DN and ER on the right side of the BTR instruction is not on. There is no BTW instruction. We've swap modules with no luck. Any idea?
Thanks,
John
I know when using 1794-IE8 with a PLC5, you need a BTW to configure the card on 1st scan, so when you power up with a new card, it gets configured automatically. It's probably the same with a SLC. Get a manual for the 1794-IE8, and the 1794-ASB from ab.com and check this out. The BTW probably needs to happen to set up the voltage/current selection for each input channel.
Also, make sure your 1794-ASB isn't faulted. Most of the time it should be configured to allow the processor to restart it after a fault. BE SURE YOU'RE LOOKING AT THE CORRECT MANUAL FOR YOUR SERIES/FIRMWARE ASB. A/B has changed some of the functions of the dipswitches at least twice over the years.
Hope this helps, Paul C.
this sounds like the processor might not be scanning your rung ... hard to imagine why it would have worked before a power cycle but not afterward ... but it's easy to check ... if you're not sure how, just copy the rung into the very top of Ladder File #2 ... this one is always scanned on an SLC system ...
if all else fails, think about posting your .RSS file ... maybe we can help you spot something ...
Sounds like the IE8 is not configured
I Think the IE8 series B needs a configuration block written to it in order to work See Pic
If you can find no BTW instruction then do a search for the corresponding #M file as it may have been programmed in ladder rather than using the BTW instruction
Does anyone know of an AB publication for RIO BTW/BTR to the 1794IE8, The only literature I find on AB site is PLC-3 & PLC-5 I am using 1747SN, I...
13,543
The problem started with an error 208 in my PV900 after a program change and download to my slc 5/04. The logic had worked for over 2 years...
2,772
Hi currently my work parther an I are working into trying to visualize a set of values on a PanelView 550 that is connected tru a RIO connection...
6,529
Hi, I am trying to get some flexi IO communicating. The scanner has its steady green light on The G file is all the default values.The first two...
5,229
Hello all, I see that the Block Transfer Read instruction can read a max length of 64 words I have a Hilscher gateway to map DeviceNet Slave to...
852