1756-L72 firmware upgrade
Status
Not open for further replies.
sifis said:
...Thank you for the advice.
Good advice is usually based on good information. Usually.
I am not worried in the slightest, my friend, and good luck with your endeavours.
G.
Be advised when you flash the firmware, it will delete the program that is in the processor. Be sure you have an up to date backup of the program BEFORE you try to update the firmware. You will need Studio5000 with a version number that matches the firmware revision to put the program back in the processor after flashing it.