1762-OB16 for ML 1400 Connection
caleno
Mar 2010
NJ
36
Hi I need to wire module 1762-OB16 (DC Source Output Module). The module is connected to my ML 1400 PLC. I am a bit confused with the wiring, on page 8 of the installation manual, link below (Field Wiring Connections) it points out a 24V DC(Source) connected to VDC+ & DC COM terminals. I am wondering whether I need to provide an external 24VDC Power supply and connect it to these two terminals? Or this is an internal connection to the PLC, thus I would not need an external power supply? Thank you in advance.
https://www.ideadigitalcontent.com/files/11994/ID-SPE-v1-1762-in011_en-p.pdf
Yes, you will need to connect a 24VDC source to these terminals. The OB16 is a transistor output module, and needs a 24VDC and 0VDC connection for the transistors to function.
Does anyone know what type of thermister for the CJC on a 1762-IT4 thermocouple card? I have searched everywhere and can not find. I can not see...
626
Hi every master,Recently i met a fault about 1762-L40BWA 1,When i get the PLC, The Fault light is lighting, I am not remember the fault message,I...
720
Hello everybody and master,I met a problem about ML1200.It is described as below: 1,When i got this PLC,The FAULT light is lighting, My computer...
1,113
I have 1769-IF4 module and 1766 micrologix 1400 series B controller, when connecting Analogue input in module it's showing maximum values of...
1,699
With the ML1100 being a Legacy product, this is something of an academic discussion. I have an ML1100 with two expansion modules - 1762-IF2OF2...
867