My configuration goes like this
Main PLC
1756-L72
1756-EN2T
1756-EN2T
I/O
Servo
Panelview Plus 600
Stratix 5700 [Linking to Remote I/O unit and servo]
Remote I/O
1769-AENTR
I/O
Panelview Plus 600
I have configured all except the Panelview Plus 600 on the Remote unit
I notice, 1769-AENTR does not appear in RSLinx [but it is communicating with L72 and I/O are functioning]. I am connecting the remote Panelview Plus 600 from the second port on 1769-AENTR.
So I am puzzled about the usage of second port of 1769-AENTR.
Questions I have is,
1. Why 1769-AENTR and its I/O does not appear in RS Linx.
2. What is the purpose of 2nd port on 1769-AENTR, can it be used to connect a HMI [Panelview Plus]
I am using Studio 5000 V21 with RS Linx Ver 3.60.01 and FT View Ver 7
Appreciate any help on this.
Thank You
Best Regards
___________
The EN2T is 192.168.1.6
1769-AENTR is 192.168.1.51
Panelview Plus is 192.168.1.55
Didn't use any gateway on the Panelview, but tried with 192.168.1.1. Nothing brings the AENTR and Panelview with IP set as 192.168.1.55 on RS Linx.
My other Panelview plus with IP set at 192.168.1.65 and the rest of the modules are visible on RS Linx
Thank You
This is a new project and it is the first time I am using 1769-AENTR.
After installing the required ADD-On-Profile, I was able to insert the module and configure the I/O in the offline project file. Upon downloading it to L72, AENTR I/O was responding well even though it doesn't show up in RS Linx. [Good enough for I/O]
But I can't download my ME application file to the PV Plus as it is not visible in the network.
Thank You
_________
install new EDS
Hi Osman,
Selamat Hari Raya,
I didn't add the EDS file as I thought the AOP installation will fix it. Anyway I will try that as well. Normally a yellow question mark appears on RS Link when a matching EDS is not registered. But for this case nothing shows up
Hi Osman,
Selamat Hari Raya,
You're right. EDS most likely isn't the issue since your PC isn't seeing it at all.
How did you set the IP address on the AENTR? Downloading the project does not set the IP address for those. You can do it with the dip switches on the device, then use the web based tools or via BOOTP.
Oops,
There was a bad Ethernet cable connected from the switch to the programming port of the machine. After isolating it everything works as it supposed to.
Shawn,
To answer you regarding IP address setup - I did set the last octet of the IP Address on the dip switch before downloading the program to L72.
Thank You
Hi everyone, I recently put in a 1769-AENTR, and where it is installed has had a couple power outages. Every time when the PLC comes back online...
695
Dear All, If you could please help me with the following issue it would be very helpful. Trying to solve this for the last week. I've a L33ERM...
1,253
Is anyone else watching AB 1769 1794 1734 pricing on ebay, or am i the only one??? 1769 AENTR for $4,000.........From China........Its getting...
2,041
3x 1769-AENTR being polled by 5069-L330ER PLC. AENT modules are freezing approx once per day each. Loss of communications from perspective of...
1,687
Hello everyone, I am in the beta phase of building a SCADA system. Currently planning to use Inductive Automation as our SCADA platform, but...
2,143