1769-AENTR Type 3 Code 16 Fault Help
Bysons
Jul 2020
Winnipeg
Hi all,
I have recently upgraded a PLC 5 to a 1769-L33ER and 1769-AENTR. It is two panels, back to back, with the L33ER in one, and the AENTR in the other, communicating on a larger PLC network. None of the existing panel wiring was changed or swapped out, strictly the PLC hardware.
Since installation, we have had a constant, intermittent Type 3 (I/O fault), Code 16 (I/O module connection failed on required module). And this fault code references module AENTR:7. On the AENTR rack, it goes AENTR processor, IA16, OW16, IA16, PA4, OW16, IA16, OW16, IA16, OW16, end cap. The PLC is for a refrigeration system, and the AENTR is controlling the solenoids (directly from the relay outputs, no interposing relays), as well as contactor coils for fans. The fault occurs randomly, but is consistently the exact same AENTR:7 module fault. It could happen 6 times in a 12 hour period, or it could happen once, or not at all. It doesn't appear at the same time, and there are no other visible patterns we can find for when it occurs. The only way to reset and clear this fault is to power cycle the PLC's and then clear the fault and put back into run mode, which is a pain for the operators as the panel is across the plant from their control room. I've chatted with my local Rockwell rep numerous times, as well as calling Rockwell tech support, and nothing we've tried has stopped it. I will try to lay out all of the things we have tried, and I am hoping someone has a solution they can think of or found!
- We thought at first there was a communication issue between the main processor and the AENTR, we've tried connecting them directly, to different switches, changed settings on the switches, all to no success or effect. As far as I can tell, it is not a network issue causing the fault.
- We then thought we had a bad card/bad connection. I swapped all of the IA16 and OW16 cards around randomly and made sure all connection tabs were secured correctly. We swapped end caps from the main rack and this rack, and swapped PA4 cards from the main rack to this rack. All of them never stopped the issue, and the error code module never changed, still AENTR:7.
- We looked into maybe the RPI being too fast, so we maxed it at 750ms, which can only be changed on the cards, not the AENTER module itself. We thought maybe the problem was happening quick enough that we could basically ignore it for 750ms, and it would avoid the fault. No such luck. We tried turning off the Major Fault on Connection loss as well, but all it did was still fault (connection loss), and we just wouldn't know it was faulted instead.
- The 120VAC supply for the PA4 on the AENTR rack actually came from the other panel, so we thought there could be noise or EMF of on that line, so we installed a 120VAC filter right next to the AENTR rack. After this change, we did not see the error for a whole week, the longest it had gone before that was 2 days. We thought we solved it, but it popped back up again, and is happening every day again. There is a 480-120VAC transformer in the AENTR panel, so we tried taking the 120VAC off that transformer to the filter instead of from the other panel, and still did not stop the error.
- Rockwell recommended that for inductive loads, such as solenoids, on a relay output card, should be surge suppressed. They had no suppression from the PLC5, and I've rarely encountered needing surge suppression on AC stuff, but we decided to go down this road. We chose RC suppressors as the best method to try to quiet any noise from the turning on or off of a solenoid. These aren't exactly cheap, and we have 48 solenoids total, so we decided to order one cards worth, and try it on the card we think is the issue. We believe since the code is always on module 7, that OW16 in slot 6 must have the noise on it, which is then dropping the connection to card 7. So we installed surge suppressors on all 12 solenoids on slot 6. Again to no avail.
Where I'm currently at is swapping all the cards around one more time, seeing if maybe the fault moves to another module and we just didn't catch it moving (which I'm 99% positive we didn't see it move the first time), as well as putting in interposing relays for all of the output cards to ensure that no external noise can get on the backplane. I'm running into desperation mode, and running out of straws to grasp at. Hoping someone here has encountered this issue and can put me on the right track! Sorry for the long read, but thank you!
1771 I/O was heavy-duty and metal-encased and generally less sensitive to voltage spikes and electrical noise than any modern I/O platform.
The error code you are experiencing is entirely consistent with back-EMF voltage spikes from un-suppressed solenoids. I agree that it's more common with DC loads, but ordinary RC snubbers really are the first thing you should install on solenoids if you're experiencing any noise-related errors in the I/O system.
I agree that it's unusual to have the fault on Slot 7 when the outputs are wired to Slot 6, and agree that working outward from Slot 6 to the adjacent slots is the best course of action.
1769-AENTR Faults
Over the weekend we decided to switch all of our solenoid outputs to interposing relays to eliminate the solenoid noise from entering the output cards at all. They now come from a different 120VAC source than what is powering the rest of the outputs and PA4.
It lasted about 2 hours running like this, before faulting again, but this time with a new fault code. Type 03 Code 23. Which is still an I/O fault, but more related to physical connection between cards. It no longer gives me a module in the error description. In response to this, for the fourth time now, I decided to move cards around, check all my tab connections, and tried just moving the PA4 over a slot to see if there would be any change in the error or stop it completely.
In the end that too was to no avail, and it has faulted 4 times since Sunday. I'm unsure yet if it is still producing the same Type 03 Code 23 fault each time, as the operators keep resetting it before checking the fault code when I'm not there.
The only other thing I want to add, is that the output cards also power contactor coils for fan motors. Those are not on the interposing relays and are powered directly from the output card. Any chance of noise being produced by those coils?
I'm desperate for any new ideas! Thanks!
I wouldn't power anything more than a pilot light directly from a modern standard output module. Like Ken said, the older stuff was a whole lot more over-engineered and tolerant than the newer stuff, and interposing relays are a whole lot cheaper than output cards. If this were my system and I was having errors like this, installing interposing relays on everything would be step 1.
When you moved the power supply over a slot, did you make sure that all the modules are still within their power supply distance rating? For most modules the distance rating is 8. Notable exceptions include the 1769-OB32 (6 modules), the 1769-AENTR (3 modules) and all types of processors (also 3 modules). There are also a handful of specialty modules with lower ratings. Exceeding the power supply distance rating of a module could definitely cause intermittent faults.
Of course it's also possible that the module itself has been slightly damaged now. By installing interposing relays you've prevented it from getting any worse, but it may be that you're still going to have to replace the card to resolve the problem entirely.
Hi everyone, I recently put in a 1769-AENTR, and where it is installed has had a couple power outages. Every time when the PLC comes back online...
690
Dear All, If you could please help me with the following issue it would be very helpful. Trying to solve this for the last week. I've a L33ERM...
1,247
Is anyone else watching AB 1769 1794 1734 pricing on ebay, or am i the only one??? 1769 AENTR for $4,000.........From China........Its getting...
2,039
3x 1769-AENTR being polled by 5069-L330ER PLC. AENT modules are freezing approx once per day each. Loss of communications from perspective of...
1,683
Hello everyone, I am in the beta phase of building a SCADA system. Currently planning to use Inductive Automation as our SCADA platform, but...
2,137