1771-ife
bwheat
Sep 2003
LA
174
I have a PLC 5/15 with a 8 slot 1771-A2B chassis and one slot open. The slot is right next to a slot mounted power supply. Will the IFE work in the slot next to the power supply?
Yes, should be ok. I have a system PLC5/40 with bigger chassis
with analog module next to PS and it works just fine. If I had a choice I would not. Only issue may be noise. But no problems with my system.
Great. I thought I had read somewhere that I could not do that but I must have been dreaming.
as Mickey said, the power supply probably won't cause any problems ... and everything else will PROBABLY be ok too ... but if this is a critical (unsafe) system, it would be a good idea to tell us what addressing mode you're using (two-slot, one-slot, or half-slot mode) and what other modules you have installed in that chassis ... I don't have time to research the details right now, but there ARE some restrictions about what will - and will not - work ... mostly it's related to things like 32-bit discrete modules being used next to Block Transfer type modules (like your 1771-IFE module) ... if I remember correctly, in some addressing modes, the Block Transfer can "borrow" a byte from the input and output addresses assigned to a discrete module in an adjacent slot ... but then again, my memory ain't what it used to be ... if you can supply the details on your layout, I'll try to find time to check the references for you ...
Jumpers Question
Hi Folks,
While on this same subject, I am working with an old 1771 IFE A module. I have no documentation on this and am only able to find docs for the IFE C on AB's site. Maybe I'm not looking in the right place, but obviously the jumpers are configured differently. As is, I am able to read +/- 10 VDC with all jumpers set accross the pair next to the arm connector.
I am using it single ended with inputs 0-3 for +/-10V and 4-15 will need to be set for 4-20mA. Any hints would be very appreciated.
Jimmy
check here ...
and one other thing ... your inputs will actually be numbered "Channel 1" through "Channel 16" ... the "Channel 0" starting point is usually appropriate for an SLC system ... is that what you're more familiar with? ...
2 slot addressing. IFE will be located in the next to the last slot in chassis right next to the power supply. There are 16pt AC input and 8pt Relay output cards in the chasis. I think it will work. I was probably thinking about the card being next to a 32pt card. I have stepped in that one several years ago.
Jumpers Question Cont'c
Yes, input 1, etc... not 0.
My question is regarding the jumpers for the IFE A. How are they configured with respect to the input channels? I know the position I have them in works for voltage, but need to know what jumpers correspond to which inputs (there are more jumpers than channels).
Thanks,
Jimmy
Thanks,
Jimmy
Ron Beaufort said:
check here ...
Click on the link Ron provided it is the user manual for the 1771-IFE/A
Or here http://www.plctalk.net/qanda/showthread.php?t=26202
from the "silver platter" department ...
Greetings Jimmy ...
see if this does what you want ...
Hi: I recently tried connecting 2 new single-ended 4-20mA analog inputs to an existing 1771-IFE. The IFE is in a RIO chassis. The values coming...
1,422
I'm having issues saving the individual channel settings on a 1771-IFE Analog card. We recently swapped from 0-10v to 4-20ma transducers. I...
1,020
We will repair by ourselves at first by replacing few power ICs such as 78M15,79M15, 79M05 and T3055E. What is TE055E Motorola TO-252, Transistor...
1,700
Hello. Wanted to ask you seasoned vets out there about a scaling issue I'm having. Controller migration. A 1771 IFE 0-5VDC analog signal...
2,542
Hey guys, I need to replace a Allen bradley 1771-IFE-C Rev D01 analog input card as it died. It’s been a while working on AB PLC 5, do the...
1,926