1771-VHSC c/w 12 DI but 4 counters only?
ckchew666
Aug 2003
Malaysia
591
I'm checking on the 1771-VHSC module, it has 12 DI, but stated 3 per counter only. This means the module has built in 4 counters (high speed). So the rest of the DI is not for high speed applications?
Hope someone can clarify this.
Thx.
ckchew666
You keep asking about the capibilities of several different cards, but you haven't listed your application.
If you would tell us exactly what you are trying to do, perhaps we could make some suggestions. So far we are only getting little tidbits, and not the whole picture. Up to now we know you have 2000Hz inputs, we do not know what you are doing with these inputs, what is the required action that needs to take place? What causes what to happen and when?
Can you give us an application overview?
If you were to use a 1771 counter module to measure wind speed which would you use? 1771-VHSC OR IJ/IlK ?
1,924
From the manual: " Use the period/rate mode to determine the frequency of input pulses by counting the number of internal 4MHz clock pulses over...
1,863
Converting a PLC-5 to ControlLogix, still using some old PLC-5 hardware as remote I/O. My issue is I have a 1771-VHSC card in a remote rack away...
2,457
Have read most of these postings on this module I got a new one for ya One encoder with channel A wired to A1 and A2 IE Counter 0 and Counter 1...
2,472
I have an application coming up that will have 2 oil shear brakes on opposite sides of a differential. I need to be able to control a speed...
1,729