1771-VHSC for measuring shaft speed/direction?
Paul351W
Mar 2008
Northern Illinois
154
I have an application coming up that will have 2 oil shear brakes on opposite sides of a differential. I need to be able to control a speed difference across the differential by controlling the brake torque on each side.
The brake controllers will have their own stand alone controllers to control the torque requested by the PLC-5, but I figured I will have to do the speed control loop in the PLC. Both brakes have a speed encoder that I could monitor, can the VHSC module measure speed easily & quickly? I thought that using an encoder input would be better than using analog inputs from the speed sensors.
I think the PPR will be 512, and the shaft speed will be up to 1000 or 1500rpm is all, and the customer wants to control the speed differential within +/-5rpm. During some points they want no speed differential, and other times they will command a speed differential, up to around 150 or 200rpm is all.
If you were to use a 1771 counter module to measure wind speed which would you use? 1771-VHSC OR IJ/IlK ?
1,913
From the manual: " Use the period/rate mode to determine the frequency of input pulses by counting the number of internal 4MHz clock pulses over...
1,863
Converting a PLC-5 to ControlLogix, still using some old PLC-5 hardware as remote I/O. My issue is I have a 1771-VHSC card in a remote rack away...
2,456
Have read most of these postings on this module I got a new one for ya One encoder with channel A wired to A1 and A2 IE Counter 0 and Counter 1...
2,471
Hello all, I am adding a 1771 VHSC card to an existing system in order to more precisely control part positioning. The problem I am having right...
2,802