1794-ADN with 1794-IF4I
CSnerd
Nov 2008
Indiana
24
Hey All,
Having problems with a 1788-DNBO scanner talking to a rack of 1794-IF4I's via a 1794-ADN.
I used the DeviceNet Tag Generator from the RSNetworx dnt file. The status word for each module indicates that it is in "Configuration Mode (CF bit)" and Field Power is off. I have veried in RSNetworx that the Flex Configuration settings are set to I/O only. I have also confirmed that 24V is being applied to each card.
The DNBO has a firmware rev of 2.002. I have another ADN with Digital cards, those work perfect. I have swapped the ADN's to make sure the ADN is not bad. I have flopped modules and bases as well.
Very frustrating, hope someone out there may be able to help.
I have spent three days on the phone with Rockwell and they are somewhat stumped.
Any Help would be much appreciated.
Resolution
Hey all,
Found the resolution to be a couple of things.
1. The channel range settings had been reset to none.
2. The ADN had a newer f/w rev that seem to be a problem.
I have to configure new 1794-ADN Series C in my devicenet network. I have downloaded the EDS File and registered it. But while configuration in...
1,053
This is killing me. I've only got one facility with DeviceNet and don't really know much about it. We're expanding that facility, and I need to...
2,567
Here is the scenario that I am sorting through. Outputs in a flex I/O rack are commanded on off by a Foxboro DCS system logic via Devicenet to a...
2,566
I have 1794-ADN Flex I/O Adapter connected over device-net network with scanner . The I/O and network status led are blinking RED . I have...
2,325
First of all im using a softlogix 5860 processor connected via 1784 PCIDS card to the 1794 devicenet adapter. my first module is a 16 bit DC...
2,321