1794-IF8 and control logix
Donnchadh
Jun 2002
Ireland
1,004
Hi All
I am trying to set up a 1794-IF8 on devicenet with a L62 plc and I am having some problems.
I can see the all the cards a IB16, Ob16, Of8 and I have no problems. When I add in the IF8 in to the scan list it has no data bytes in the I/O count.
I cant find a manual on the AB site either.
Just hoping some one has set one up before.
Thanks again
Donnchadh
Doublecheck that part number; the 8-channnel FLEX analog module is the 1794-IE8.
When I add a 1794-IE8 to my 1794-ADN configuration it adds 16 bytes of data (8 channels x 2 bytes) to the Input assembly.
You can configure it differently (add two Status bytes, configure the Configuration bytes, etc) but that's the default.
Which revision of RSNetworx for DeviceNet are you using ? The 1794-ADN applet changed in the past several years, I think between versions 8 and 9. I'm running version 10.
Dear all, I am experiencing temperature fluctuation problem in our new IO Input RTD module, 1794-IF8. Previously, the temperature sensors are...
6,773
Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
180
I'm sure this question has been posted a thousand times on here but for me it was even funnier when I got to ask Rockwell / AB directly. My...
173
Hello, a customer i support has DH+ RIO racks all over the plant. they use 1794-asb modules. today they had a rack fault out and go unresponsive...
663
I have to configure new 1794-ADN Series C in my devicenet network. I have downloaded the EDS File and registered it. But while configuration in...
1,058