Hello,
i'm planning to use 1794-IJ2 frequency module for the first time in my new project.
My questions are:
1)can i use this module in place of dynalco speed monitor?
2)is it necessory to connect 2 inputs in this module?cant i use single magnetic pickup probe as single input in this module?(as catalog says that this module calculate speed with two probes only.)
3)what is the difference between gate input and frequency input?can i connect any input to frequency input?http://www.plctalk.net/qanda/member.php?u=33571
Yes, but you will have to do some math to get speed. Module gives you frequency and direction.
No
Yes a single input is ok. Each channel has two inputs frequency and gate. Frequency input is used to calculate frequency and the gate input is used to determine direction.
Gate input is used to determine direction.
Not sure what you mean here, see manual for devices that can be connected. Link below for manual.
http://literature.rockwellautomation...m011_-en-p.pdf
I currently use a 1794-IJ2 to read in a IEC 1+ (Namur) frequency signal (+24v & F Pins) and have been asked to build a similar system but using...
1,172
Is there a way to convert this module to a counter card?
1,845
Greetings, I'm putting a 1794-IJ2 (Frequency Input Module) in a small Flex I/O drop from a ControlLogix PLC. The user manual gives programming...
4,391
Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
179
I'm sure this question has been posted a thousand times on here but for me it was even funnier when I got to ask Rockwell / AB directly. My...
172