1794-OA16 Relay output module off-state voltage
bigLee
Jun 2018
Florida
77
Hello,
Is anyone familiar with the off state voltage of the channel for this module? I have it wired up according the page 14/15 of this manual:
https://literature.rockwellautomation.com/idc/groups/literature/documents/in/1794-in103_-en-p.pdf
When energized I get 120VAC L1 to L2. When de-energized it drops to 117/118 VAC.
Is this normal? Seems like that would still keep equipment connected to that channel powered.
I haven't tested with relays yet but figured I'd throw it out there to see what anyone thinks.
Thanks for any information.
An OA16 output is not a relay output it's a triac (Solid State)
for relay it should be OW
relays don't have an off state leakage
That's not really true. Off state leakage with a relay output is less than with a triac output though, since it is caused by leakage through a surge suppressor installed in parallel with the relay contact -- typically an MOV.
Mickey, thanks for the info. Thanks everyone. Just tested some pilot lights and a conveyor and everything works as with the 1771 module.
Thanks again!
As long as the lights are incandescent, LED's might be a problem with solid state outputs (leakage).
This is true. I had LED pilots running on a triac card. It was just what I had laying around at the time. I want to say I added a 1K resistor to keep the LED from glowing dim when off.
Hey guys, Im currently using the above flex IO to turn on two outputs these outputs go to two flashing red beacon lights. Here's the scenario: My...
1,711
Hi Guys I am using 1794-OA16 120VAC DO, when the output point is actived, I will get 120VAC, and I still got about 24V when the output was off...
2,902
Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
172
I'm sure this question has been posted a thousand times on here but for me it was even funnier when I got to ask Rockwell / AB directly. My...
170
Hello, a customer i support has DH+ RIO racks all over the plant. they use 1794-asb modules. today they had a rack fault out and go unresponsive...
657