1794ACN15 Flex I/O Adapters Hanging

jimdavie

Member
Join Date
Nov 2008
Location
Wishaw
Posts
6
Hi,
We have a 15 year old installation with 6 lines of 7 flex I/O adapters hanging off dual redundant PLC 5's. We've never had any major issues apart from the odd card failure until now. We're now starting to get various items of plant faulting because the PLC code is showing an output firing but it's not reaching the field item via flex I/O. A reset of the supply on the adapter for the particular I/O module cures the issue, there's no need to cycle power on the particular card. All the BNC connections look to be sound. I don't think it's PLC related because we have 6 identical lines and a couple of them are showing issues. As with any intermittent fault it's a process of elimination. We've cleaned all the card pins and bases as we though it may be an issue with H2S attack on the connections (sewerage plant). We've only just discovered that an adapter reset does the trick so were considering a change out of all 7 adapters next.
Anyone experienced similar?
Thanks
Jim
 
Morning Jim,

We have one major installation with 1794ACN15 adapters, and the main issues we get are with the BNC connectors, usually find that once we have an issue, we then have a blitz to check and remake/replace the connectors. But then we could have a vibration problem, rather than corrosion.

H2S could be a problem, especially on waste water plants of that vintage.
What is the ventilation like where the racks are mounted?
Are some more enclosed than others, hence getting more exposure to corrosion?
I have seen other PLCs attacked by corrosion in WWTP and not always obvious on the electronics. If you have one or two that are susceptible, change the adapter but also check the ventilation...
 
Thanks John,
Yes might be an idea to have a good look at he BNC's rather then just check they're tight. All that adapters are in similar control panels with reasonable ventilation/cooling. We've had to change a large number of small relays in the past due to H2S attack just hoping that flex I/O isn't going the same way.

Jim
 

Similar Topics

I have been getting 1794 ACN15(R) for my FlexIO remote racks in the past. I recently received a 1794 ACN instead. It looks similar and I ASSumed...
Replies
2
Views
3,203
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
0
Views
56
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
132
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
111
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
100
Back
Top Bottom