We have a piece of equipment that is very important to our overall operation. We lost communication on Friday that caused some issues. My question is , how difficult would it be to have 2 - 1756-ENBT EtherNet modules in one rack , so if one connection or module would fail , the other would take over. Would there be any additional code to write ? Could we have the same IP Address for both modules ?
Thanks , and have a good weekend.
It depends on the HMI software.
You definitely cannot have duplicate IP addresses. And I strongly recommend against trying to roll your own IP swapping code inside the Logix controller. I have been down that path and was eaten by a grue.
I did a system with RSView32 and the RSLinx Classic OPC Topic Switcher. That worked well. I don't know of a way to do a similar thing with Factory talk View.
Similar Topics
please using the usb can i assign any ip address that i want ?
Replies
4
Views
164
Hi, I want to exchange data between two L55 PLCs using ENBT PLC1 is the main PLC and consist of 1756- CNB, L55 CPU and ENBT. Five remote I/O racks...
Replies
7
Views
1,042
Hey guys, I'm not super familiar with Cnet, so I'd like some insight from people with more ControlNet experience than I. We have a controllogix...
Replies
4
Views
907
I am looking into an ethernet drive network system using a Logix5000 system Version 20 and noticed that on the general tab of the properties of...
Replies
1
Views
1,142
I wanted to confirm with the Gurus that a 1756-ENBT can not create raw sockets. I'm using Rockwells Process Library's T_Sync to connect to an NTP...
Replies
3
Views
2,006
Back
Top Bottom