2 pole GFCI Breaker
jimtech67
Jun 2002
New Jersey
505
I am looking for 2 pole 240 VAC 30amp GFCI Breaker that can be panel or din rail mounted.
Cannot seem to find one. Any know if this exists ?
We typically use ABB, such as:
http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/90022ebf6f32c51cc1257a170033ce4f/$file/2CSC423011B0201.pdf
Be careful with your terminologies here. Use of the term "GFCI" is narrowly defined as being a "Class A" ground fault protection device, which is intended for PERSONNEL protection and trips at a MAXIMUM of 6mA of ground current. The IEC style "ground fault breakers" described in the pervious posts are not UL listed as Class A, so they cannot be use for the same purpose.
So start with why (or if) you really NEED a Class A (GFCI) device. Many people tend to over interpret this requirement. If you read the NEC, the only times that you need a GFCI is when you have PLUG-IN equipment that is or could be in a wet invironment, i.e. bathroom, kitchen, outdoors, or if it is a swimming pool or spa, or if it is a carnival or circus. If it is one of these cases, for example a 240V portable pump that is going to be plugged into an outlet, then you will be forced to buy a small CB load center to plug the breaker into, because Class A GFCI breakers must connect to a Neutral bus, not just a ground bar. You can however get very small load centers that only hold one 2 pole breaker, often referred to as "spa panels" because that is a big market for them.
If you have a simpler requirement for "Ground Fault" protection on equipment, but is not related to personnel protection, that does NOT necessarily need to be a GFCI (Class A) device, in which case the IEC versions (if UL listed as a circuit breaker) may suffice.
I agree with Jreaf.
A ground fault device is to ensure if you contact one phase and an earth it will trip the power before you receive a shock. This is done by measuring the balanced current
in a phase to phase system contact between phases makes you the load with no phisical ground connection. Not good.
Hello Everyone! Short and simple questions, I have one PLC output, that I want to wire to 10 different devices. Does anyone know of a relay that...
2,411
We are installing 20 foot direct burial fiberglass light poles, and we are mounting speakers for a pa system on the pole about 12 feet up. Can the...
1,821
Hi I have an IEC motor 4pole motor 50Hz 5.5kw. It is stamped with 1540rpm. Is this even possible for a 4-pole motor?
3,327
I apologize in advance if this is off-topic, but I really need to understand what's going on... While doing some renovations, it was found...
20
5,574
I am designing a machine for use in the European Union. The machine will include a Ropex heat seal controller that will receive a 230VAC single...
40
7,353