24 Volt DC Inrush OverCurrent on PLC
ryanweber101
Oct 2008
Indiana
This has thrown me a curve ball so I'm looking for someone smarter than myself to provide me an answer.
I have a 24 Volt 1769-OB16 DC output card connected to 14 contactors. I am staggering when they pull in but unfortunately the inrush is 91 VoltAmps which correlates to 3.79 Amps given the system is 24 volts. The output card is rated to 2Amps for 50 milliseconds, but the inrush seems as though it could be more than the card can handle. How long does this inrush last? Anything under 10ms means the current set up will work, if not I need to either upgrade my output card or use a different network of contactors.
Respectfully,
Ryan
I think that you will fry that sucker....it would be better (also read more panel space & $$) to put in sone small relays that then turn on those contactors....just my thoughts.
David
I was thinking along the same lines; I was just hoping to save my panel builder from having to just about rewire the whole system.
Thanks for the input.
Just spoke to our other tech guy here, said he's seen this problem in the past and took that course to fix the problem as the inrush is roughly 100ms.
Which ever route we go we need 14 relays and pretty much the next day.
Any idea on the Amp draw these will have?
If that's for the whole lot I will suggest this to our engineer.
I really appreciate the help as we are up against the wall time wise.
Take a look at these relays, I have a situation similar (3.9 amps at 24VDC) to yours and my output cards fail regularly. On the second machine that I did, I went to 240VAC coils with interposing relays. It is still hard on the relays but my output card is safe.
Hhttp://web2.automationdirect.com/adc/Shopping/Catalog/Relays_-z-_Timers/Electro-Mechanical_Card_Relaysave a look at these,
I have these in stock from Phoenix Contact:
http://eshop.phoenixcontact.com/phoenix/treeViewClick.do;jsessionid=JLqJj6RxT1FtX4ppCp8nQ101Q4dK6PBjrpKLsdQ8Gp1s4q20RPzt!-324031627?UID=2967060&parentUID=null&reloadFrame=true
If you're in Northern Indiana, PM me and I can quote you.
Can anyone recommend a flexible 600-volt shielded ethernet patch cable? I have used them from Allen Bradley / Panduit before and they are too...
117
Hello, I am very new to the plcs and am working on a project that requires a fixed mount barcode scanner to scan packages as they move along a...
206
Good afternoon, This one may sound crazy. I have a device that is configured to outputs a 0 to 10 volt signal. the scaling is 0 - 0 and 10 -...
1,660
Dear All, 3 phases (380-400 volt) are needed for my small lap in my garage. Normally there is one 1 phase 220-230 volt in my garage but I would...
31
6,717
We are installing 20 foot direct burial fiberglass light poles, and we are mounting speakers for a pa system on the pole about 12 feet up. Can the...
1,831