HI friends, I have a Micrologix 1500 (1746-LRP) connected to a PV 600 (2711-B6C5 PV600 Color Key/Touch, FRN 4.10-4.xx) thru channel 1 DH 485. We like to add a PV 1000 (2711-T10C3) to the set up. What type of interface module do I need to make this work, and what type of communication do I need. This is the first time that I’m going to be adding a 2nd HMI, so any pointers are greatly appreciated
Thank You
I’m a little confused by the set up. This is what connections I have came up with please correct me if I’m wrong.
· From the PV 1000 I would use a 1761-CBL-AS03 cable, connected to the RJ-45 port on the PV 1000 and the Phoenix port on the AIC converter.
· From the PV 600 I would use a straight thru DB9 connected to the RS-232 (DB-9, DTE) Communication Port on the AIC
· From the ML 1500 DB9 port I would use a 1761-CBL-PM02 connected to the 8 pin mini on the AIC
Also with the PV 1000 being about 75 ft away what is the best cable to use for the connection to the AIC?
That sounds correct to me.
Mickey thanks for the info. As the Pv 1000 is going to be at about 75 ft away from the ML and PV 600, I'm thinking about puting the AIC with the ML and PV 600, is it safe to run 75 ft of the 1761-CBL-AS03 cable from the PV 1000 to the AIC
I'm just saying that I dont have any other way of running the connection if I put the AIC in the Panel with the PV 1000 then I have to run the cable from the PLC and the PV 600, to the AIC
Has anyone else come across a problem when the trying to select a tag from the browser in FactoryTalk when you know longer are using a second...
3,417
Hi Folks. I am gearing up to add a 2nd identical HMI to a project. This 2nd HMI will basically be an exact clone of the 1st one. The equipment...
269
My laptop: Windows 7 Pro Factorytalk View ME 10.00.00.290 (CPR9 SR10) patch 03. I load a runtime application version 10.00.0 and work just fine...
1,098
My client wants to use a new 5069-L320ER to replace a Micro1500, but wants to keep the 1769 I/O. Planning on using the 1769-AENTR for a 1769...
2,167
I have a VBA on an alarm banner that calls a large number of pop-ups alarms based on changes of digital PLC tag value. Problem is that when the...
2,337