3-point or 1-point calibration
Charbel
Jan 2012
Beirut
307
Dear,
I need to know if it is better to ask for 3-point calibration for the radar type level transmitter or 1-point calibration is enough.
radar type level transmitter is used in diesel bulk storage tank and a accuracy of 0.1% is required.
contractor is submitting 1-point calibration with +/-2mm accuracy, in some cases, I have a tank as high as 12 meters.
kindly advice and clarify what is really needed.
thank you!
Charbel
It seems that a 0.1% accuracy in 12 meters would be:
12 +/- 0.1% x 12 = 12 +/- 0.001 x 12 = 12 +/- 0.012 meters = 12 +/- 12 milimeters
So a 1-point calibration with +/- 2 mm accuracy would be even better than your required 0.1% accuracy.
Notice that at a level of 2 meters, the 0.1% accuracy requirement will be equal to the +/- 2mm error. At all levels above 2 meters, the +/- 2mm will be more accurate than your requirement. Below 2 meters, it will be slightly less accurate.
I have seen 5 point calibrations on different pieces of equipment and I would like to do something like it in Step 7. I have a weight scale that I...
2,809
Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
90
I have a bunch of tags in Historian/VantagePoint that off by one decimal point. I looked into the HMI displaying the same number, and the HMI is...
128
Good morning, I have a Emerson/GE PLC with Cimplicity SCADA. I need to export data of a specific point/object to a CSV file and load the CSV file...
306
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
157