Hi ,when i check the 4-20 ma output from flowtransmitter with multimeter ,it can shows 4 ma , but when i check with process meter it only shows 2ma instead of 4ma , and in siemens plc 1200 analog input also shows the same as processmeter as 2ma ,what will be the issue ? for all the values from 4-20 ma it follows the same ,in 20ma plc can read lesser than 10 ma .Is it because of the load resistor issue on the flowtransmitter?