phuz
Member
I have success using this safety relay with the add-on profile, but unfortunately some of the processors are not up to v20(or higher) yet (and they can't be upgraded at this time because of the customer's corporate policy). I set up the explicit messaging and the READ is working fine, but trying to WRITE back, I am getting "Attribute value isn't allowed to be set" from the MSG instruction.
Also, when I add a RESET in connected components and set the input for the first communication channel, I get a fault on the safety relay that says "Type 05 - Internal Safety Synch Fault" and I cannot find any reference for this fault. The FAULT LED is solid red.
If I hover over the fault, it says host detected safety processors unresponsive. First off, this isn't even a safety processor, so I am not sure why it thinks that.
This is my first time using one of these, so I am learning as I go.
Here's the fault view:
(Fault Index 06)
(Type 05) Internal Safety Synch Fault
(Code 18) Host detected safety processors communication lost
(Fault Index 07)
(Type 05) Internal Safety Synch Fault
(Code 00)
(Fault Index 08)
(Type 05) Internal Safety Synch Fault
(Code 00)
(Fault Index 09)
(Type 06) Configuration Fault
(Code 20) Host detected safety processors did not respond to configuration step
(Fault Index 10)
(Type 06) Configuration Fault
(Code 20) Host detected safety processors did not respond to configuration step
Also, when I add a RESET in connected components and set the input for the first communication channel, I get a fault on the safety relay that says "Type 05 - Internal Safety Synch Fault" and I cannot find any reference for this fault. The FAULT LED is solid red.
If I hover over the fault, it says host detected safety processors unresponsive. First off, this isn't even a safety processor, so I am not sure why it thinks that.
This is my first time using one of these, so I am learning as I go.
Here's the fault view:
(Fault Index 06)
(Type 05) Internal Safety Synch Fault
(Code 18) Host detected safety processors communication lost
(Fault Index 07)
(Type 05) Internal Safety Synch Fault
(Code 00)
(Fault Index 08)
(Type 05) Internal Safety Synch Fault
(Code 00)
(Fault Index 09)
(Type 06) Configuration Fault
(Code 20) Host detected safety processors did not respond to configuration step
(Fault Index 10)
(Type 06) Configuration Fault
(Code 20) Host detected safety processors did not respond to configuration step
Last edited: