I have a PE with 5 wires...L1+, L1-, com, n.c., and n.o. My question is should I connect the com to the L1- terminal and then run my n.c. or n.o. to the input of the plc? (24volt PE)
thanks
 
That will work if you have the (-) terminal of your input module connected to the same common as the power supply. Otherwise, you will probably need to connect the COM wire to the (-) terminal of your input module. They should have wiring diagrams in the documentation with the PE.
 
different PE's with 5 wires can have different uses
Lease post the switch MFG and No' next time
 
As your sensor has volt free contacts, you can connect the com terminal to what ever supply voltage your photocell is powering, be it an interface relay, indicator or plc input.
 
So if I connect the com term to the plc, what do I do with the n.c. or n.o. wiring? Connect it to the + or - of supply?

thnaks
 
I got it working correctly... just connected com to + and the n.o. wire to plc input. Thanks for all the replies.
 
Hi matlark,
As you see giving the details help a lot more.
Some sensors with 5 wires - the fifth wire is tied back to change the sensor to NPN - that is why more details are always needed
 

Similar Topics

Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
265
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
Replies
1
Views
86
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
Replies
1
Views
977
What's everyone use for I/O drawings on new installs. I am trying AutoCad Electrical, but can't download it due to a MS Office application running...
Replies
11
Views
1,312
I've been tasked with adding a 3-wire pressure differential transmitter to a system and drawing up the wiring to an existing PLC board. The...
Replies
7
Views
787
Back
Top Bottom