5069-serial AND SLC-05 serial radio issues
snakes79
Nov 2015
Illinois
17
Hello friends.
Old PLC: SLC 5/05 1747-L552 connected to a Dataradio T96SR radio.
New migrated PLC: 5069-L330ER with a 5069-SERIAL module. FW: 32.011 SERIAL module FW: 2.012
This PLC is a Master PLC, driving 20+ slaves (mostly MicroLogix controllers, and a few compact logix processors with the 5069-SERIAL)
SLC program is converted to the compact logix. The compact logix works well, BUT a few of the stations do not message 100% of the time, and sometimes fail completely. When plugging the radio back into the original SLC processor, the messages pick up, and continue on pretty much flawlessly.
The error code on the message is: connection failure, 16#0001, extended code: 16#0000_0204
Customer wants to use the new processor that they paid dearly for.
Any ideas? AB tech support couldn't really steer me in any direction.
Can you post screenshots of the serial port config for the SLC, and same for the 5069-Serial expansion module? I'm not familiar with the latter but lets see if anything stands out.
Serial over radio can be a finnicky beast. If the serial stream gets any delays or interruptions, the radio will send partial packets of data and the slave will not interpret them properly.
Was the original PLC using "DF1 over Radio"? This differs slightly from standard serial DF1, in that NAKs and ACKs are not sent (i.e. only Request and response messages)
compact logix settings:
RPI: 80 ms
station address: 99
transmit retries: 3
ack timeout: 40 (800ms)
reply message wait 15 (300ms)
CRC error detiction
So in the polling routine with my messages, drop in an AOP of the 5069 - serial module, and populate it?
What I got out of that post, is that you cannot set the channel #1 as a DF1 master until it has the correct firmware/AOP?
It is setup, Linx sees it as the correct firmware. It even talks for the most part, with exception to a few nodes, the messages error out.
The T96SR uses a carrier control process where the RTS line turns the radios transmitter on. There are a few settings that need to match between the radio and the PLC so you have some homework to do. Get a copy of the radios manual. What you need to pay attention to things that are related to the RTS and CTS lines on both ends.
Thank you for your help. So possibly a radio setting change might help with this issue?
I'd take a step back and look at some of the basics.
Are the cables correct?
Is the pinout correct and are all of the needed lines going through (remember, you need Transmit, Receive, RTC, CTS and ground)?
Do the serial port setting on the radio match the port settings on the PLC?
Are there any diagnostic LEDs on the radio modem I.E. TX, RX, etc... and if so are they responding accordingly?
In my view, the best way to diagnosis an problem is to first understand how everything is suppose to work. Sometimes the problem is a very simply one but if don't know how it works you could be looking right over the top of it (been there done that many, many times).
I have a new L306 CompactLogix running V33 with a 5069-Serial module in order to send data through RS-232 to a Sato S84EX printer. I'm unable to...
1,330
Does any one have a copy or a source for the v2.012 AOP for the 5069-Serial. If I go to the product compatibility and download center for...
1,437
I am starting up a new RTU using a L306ER with a 5069 -serial to a Serial radio using DF1 Radio Modem Protocol. I only used it for reading to get...
1,455
Hi all! I'm using a 5069-SERIAL card for the first time, though I have plenty of experience with serial on other AB platforms. I'm running into...
3,819
Hi, Our L306ERS2 PLC controls a 5069-SERIAL A FW 1.011 programmed with Studio 5000 V32.11. When receiving data the module's diagnostic shows the...
2,203