Hello friends.
Old PLC: SLC 5/05 1747-L552 connected to a Dataradio T96SR radio.
New migrated PLC: 5069-L330ER with a 5069-SERIAL module. FW: 32.011 SERIAL module FW: 2.012
This PLC is a Master PLC, driving 20+ slaves (mostly MicroLogix controllers, and a few compact logix processors with the 5069-SERIAL)
SLC program is converted to the compact logix. The compact logix works well, BUT a few of the stations do not message 100% of the time, and sometimes fail completely. When plugging the radio back into the original SLC processor, the messages pick up, and continue on pretty much flawlessly.
The error code on the message is: connection failure, 16#0001, extended code: 16#0000_0204
Customer wants to use the new processor that they paid dearly for.
Any ideas? AB tech support couldn't really steer me in any direction.
Old PLC: SLC 5/05 1747-L552 connected to a Dataradio T96SR radio.
New migrated PLC: 5069-L330ER with a 5069-SERIAL module. FW: 32.011 SERIAL module FW: 2.012
This PLC is a Master PLC, driving 20+ slaves (mostly MicroLogix controllers, and a few compact logix processors with the 5069-SERIAL)
SLC program is converted to the compact logix. The compact logix works well, BUT a few of the stations do not message 100% of the time, and sometimes fail completely. When plugging the radio back into the original SLC processor, the messages pick up, and continue on pretty much flawlessly.
The error code on the message is: connection failure, 16#0001, extended code: 16#0000_0204
Customer wants to use the new processor that they paid dearly for.
Any ideas? AB tech support couldn't really steer me in any direction.