Hi everyone. i am needing to add a 7-day on/off control using a c-more ea9 hmi and the productivity 3000 controller. Need to be able to set an on time for each individual day and an off time from the HMI.
Ex. Monday Tuesday Wednesday Thursday Friday
On-4:00am Off-10pm On- 6:00am Off-10pm
Saturday Sunday
On-4:00am Off-11:00am Off- all day
I know there are system bit tags for calling hours and setting hours on the controller but Im not sure how to set up calling out each individual day. Does the clock need to be set using 24hr time or can I use 12hr? It corresponds with the CPU clock correct?
According to the Automation Direct forum, they show the following line to start DST.
Use this instruction to see if Clock Day Of Week -|=|- 7
Hi Talldude42,
Here are a couple of posts on the Clock functions of the C-More EA9.
https://accautomation.ca/c-more-ea9-hmi-series-panel-object-list-clock/
https://accautomation.ca/c-more-ea9-hmi-series-panel-to-plc-and-plc-to-panel-settings/
The C-More can be set up to use its internal real-time clock or an external real-time clock like the one in the PLC. I would suggest using the one in the PLC and updating the C-More with the tags for display.
All of the Productivity clock bits can be found in the help file. Search for clock and select system tags. This will give you a description of the tags that Aabeck mentioned above.
I hope this helps you out.
Regards,
Thanks for the reply. I didnt see this example on their forum page. Although the more I look at it the less it make sense to me...
The month doesnt matter to me for this application.
I need to use a number to designate what day of week it is correct?
Not sure what its tryinig to do at the end of the logic.
Hi Talldude42,
Regards,
Thanks I will check this out as well!
Use the compare contact.
Clock day of Week >= 1 and Clock day of Week <= 5 then Weekday
Clock day of Week > 5 then Weekend
Regards,
Garry
What they were doing at the end of the example was Set a DST bit, then add one hour to the hour.
Just compare Clock Day Of Week
1 = Monday
2 = Tuesday
3 = Wed....
7 = Sunday [Which is sort of odd, as most platforms I am used to Sunday = 0]
Here are some samples of how I have it set up. My question now is, how will the controller know the difference between am and pm? Or will i need to input time on a 24hr clock instead of using 12hr? Do i need to change the setting on the controller clock itself aswell?
The PLC clock is 24 hour format
If 0 to 11 then AM, 12 to 23 PM
If 0 add 12 for 12 AM
If 13 to 23 subtract 12 for PM hours to display
1 = Monday
2 = Tuesday
3 = Wed....
It irritates the hell out of me that they number their bits 1-16. Bit numbers start at zero, period, end of story. They're doing it wrong.
One ting they are doing right is pricing their software to $0.00
If a PLC maker wants to sell their PLC's more make the software available free or cheap, not another $6,500 for the full edition after buying the rack, CPU, power supply & IO.
They have a lot of things right. The analog modules with mA right on the front of them are so cool.
Hi, I have a 1500 that controls a station with diferents warehouses, but i also have a 1200 that controls one of those warehouses, i have been...
289
I'm preparing architecture for a fairly complex control system (technology stack is Beckhoff, so OOP etc is available). The system has many...
367
Hi, I've seen this on many machines over the years. Usually on the main control panel there are two buttons, one for control power on and one...
2,244
Needing some help. I have a machine that was put in storage and has ended up in my lap. It had a 5/02 originally but the card was pulled and I...
1,421
I have PID temperature control which will connect to Beckhoff EL4004(0v-10v). How I can program it to let EL4004 to control the temperature?
2,638