A/b 5/40e fault code help
spice_miner
Member
Join Date
Aug 2006
Location
Iowa
Posts
45
I had a major error today on a 5/40E, anybody know what the fault was? I tried looking it up in the help section of Logix but no go. Here is the crash report:
Wed Aug 05 09:23:55 2009 from RSLogix5 v7.10.02.01
Diagnostic Data for Processor PLC5/40E Series E Revision E.2
Domino Plug 1 Firmware Series/Rev: A/Q
Fault logged by microprocessor: UPB
Error string: ".....up2: hardware fault=0008b at address 1871a"
D0 = 0x00000100 A0 = 0x00202590
D1 = 0x00000000 A1 = 0x00200428
D2 = 0x00000033 A2 = 0x00206C6E
D3 = 0x00000005 A3 = 0x001988B6
D4 = 0x0000E3FF A4 = 0x0019DD30
D5 = 0x5FF67F7F A5 = 0x0020042C
D6 = 0xFFFFFFFF A6 = 0x00202598
D7 = 0x7FA5FFF7 A7 = 0x00202586
Error Code = 0x008B
Trap Offset = 0x0000
Return address = 0x0001871A
68Ks Status Register = 0x2000
Following are 26 words of stack data in hex
0000 0005 0000 000A 0019 88B6 0020 25BE 0001 85A0 0000 0101 0000 0033 0000
0005 0000 0005 0013 0000 0019 C6DC 0001 7448 0005 0020
Raw Data of above
0x198DAA 00 02 00 00 01 00 00 00 00 00 00 00 00 33 00 00 .............3..
0x198DBA 00 05 00 00 E3 FF 5F F6 7F 7F FF FF FF FF 7F A5 ......_.........
0x198DCA FF F7 00 20 25 90 00 20 04 28 00 20 6C 6E 00 19 ... %.. .(. ln..
0x198DDA 88 B6 00 19 DD 30 00 20 04 2C 00 20 25 98 00 20 .....0. .,. %..
0x198DEA 25 86 00 8B 00 00 00 01 87 1A 20 00 00 00 00 05 %......... .....
0x198DFA 00 00 00 0A 00 19 88 B6 00 20 25 BE 00 01 85 A0 ......... %.....
0x198E0A 00 00 01 01 00 00 00 33 00 00 00 05 00 00 00 05 .......3........
0x198E1A 00 13 00 00 00 19 C6 DC 00 01 74 48 00 05 00 20 ..........tH...
0x198E2A 07 07 07 0D 0A 75 70 32 3A 20 68 61 72 64 77 61 .....up2: hardwa
0x198E3A 72 65 20 66 61 75 6C 74 3D 30 30 30 38 62 20 61 re fault=0008b a
0x198E4A 74 20 61 64 64 72 65 73 73 20 31 38 37 31 61 0D t address 1871a.
0x198E5A 0A AB EA E3 C0 B3 65 75 74 FF 87 F5 CF 3A 11 9D ......eut....:..
0x198E6A 2A 46 45 D5 77 1B EB 8B E7 8F 22 FA E6 72 36 BE *FE.w....."..r6.
0x198E7A BE F8 FA F1 02 A8 50 E6 4C F7 17 0D 16 B3 07 7C ......P.L......|
0x198E8A 77 54 68 B5 E7 7C DC AB 87 D6 8F 38 C6 2A E1 1A wTh..|.....8.*..
0x198E9A BE 82 43 A8 0B AD 77 49 BC 94 A5 BC 57 D7 D0 1D ..C...wI....W...
0x198EAA 11 DF 4D 96 45 85 ..M.E.
Maybe someone on here knows how to diagnose the crash log file on a PLC-5. I for one don't. We always forward this information to AB and open a tech support case when we get them. Last time we had a series of these we had to get several of our processors firmware updated. But it was a couple of times a week problem.
The A/B tech said that it was an I/O timeout error but he couldn't elaborate. He said if I would update the firmware to K.3 from E.2, I could get more info the next time it happened. I have bricked a few devices trying to flash firmware so I am a little nervous. A $6000 processor for a paperweight would not make me happy. Anybody ever flash one?
The last time I upgraded the firmware on a PLC5, I had to get a "chip kit" that replaced eproms in the processor. I still think they do it that way rather than with a flash upgrade.
Ah-so, that's why the tech told me he would email the zip file and send me a corn chip. I now believe he said comm chip.
Hi,
Last time (only time) I had a 5/40E take a dump it turned out to be a RAM memory failure that required a complete replacement. My cost was $9,000 with an exchange of the old unit.
The firmware kit is a box of several chips. Some are for communication. I didn't get any files to download.
These processors are usually bulletproof. We have some that are over 20 years old & still chugging along.
Good Luck
BD
Similar Topics
I have a PLC 5/40E that is giving me a comm error 01E00204. It was working fine until a power outage yesterday. What does that error mean? I...
Replies
3
Views
5,729
need some help here figuring out how to find a status bit for this. I have channel 1B cofigured to rio. I have several rio racks. couple of...
Replies
2
Views
7,233
hi am a beginner in controlling the G120 VFD can you give an easy-to-understand source about controlling G120 vfd with (CU240e-2-pn) unit using...
Replies
2
Views
756
Hello Everyone, I am reaching out to this knowledgeable community with a peculiar problem I've been experiencing with a PLC 5/40E. This issue has...
Replies
16
Views
2,286
Hello I am using explicit messaging to control the PowerFlex40 E with my controllogix, I can read from the refernce and logic commands but when I...
Replies
5
Views
847
Back
Top Bottom