explicit Messaging to control a PowerFlex40E

ahmeduqat

Member
Join Date
Jul 2023
Location
canada
Posts
15
Hello

I am using explicit messaging to control the PowerFlex40 E with my controllogix, I can read from the refernce and logic commands but when I try to write values, it gives me a message 16#0010 that the Mode or State of module does not allow the object to perform requested service.

Any Ideas plz.

regards.
 
No, I just want to do it out of curiosity. I can read the command but I can't write it to the command register. I don't know what is a reason for that.
 
That drive specifically will not let you write to the Output assemblies. It requires an ordinary cyclic I/O connection and prevents you from even trying to run the drive in an incorrect, inappropriate, and unsupported way.

Other A-B drives will let you try, with SLC-500 data table emulation. But not this one, with explicit messaging to the I/O assemblies.

Welcome to the PLCTalk forum community !
 

Similar Topics

I am looking for good resources to learn more about how to message a NXR-ILM08C-EIT with a CJ2M omron plc. I am relatively new and will appreciate...
Replies
8
Views
854
Hi, Can a tag configured as a Produced or Consumed tag be read or written to with Explicit Messaging? Context: we are retrofitting an AV system...
Replies
9
Views
2,246
Good afternoon! For the past several days, I have been trying to set up this Balluff BIS018A RFID head to communicate with a Do-more BRX DM1E-M-D...
Replies
10
Views
5,561
Hi All, I am having an issue with explicit messaging. I am using a Micrologix 1100 and programing it with rslogix microstarter lite v8.3. The...
Replies
7
Views
2,559
Hello all, I am running an L43 compactlogix which is the master for a Fanuc robot with R30iB controller. I am using explicit messaging to send...
Replies
1
Views
1,637
Back
Top Bottom