Peter Nachtwey
Member
Look ma Greek letters!!!
Turning the valve on and off quickly will cause pressure spikes. This is where that thread that Norm posted a link to is useful. One can determine the pressure spike as a function of flow and volume.
The rate of change in pressure is
dp/dt = BulkModulusOfOil*Flow/VolumeOfOil
I cover this in the upcoming Hydraulics and Pneumatics.
The pressure spikes can be calculated by multiplying each side by dt and making that the update period. Because we are talking in time increments dp and dt should be thought of as Δp and Δt.
Δp = β*Flow*Δt/VolumeOfOil
β is the bulk modulus of oil which is about 160,000 psi. Flow*Δt is the same as ΔVolume
You can see the units match.
All so, you can see that if in one time period the ΔVolume changes by just 0.1% the pressure will change by 160 psi. When this is multiplied by the area, which we don't know yet, the resulting change in force can cause a shudder in the system. Therefore Δt should be kept small.
I am still waiting to hear about the existence of a counter balance valve. I am not convinced that the volume change is the whole story.
All of that and yet no specifications for the on and off times. On off times are critical for a a bang-bang positioning system. The faster Norm can turn on and off the valve the finer his control will be. Those valves are useless if it takes a 100 millisecond to open or close.fluidpower1 said:For what it's worth.
Turning the valve on and off quickly will cause pressure spikes. This is where that thread that Norm posted a link to is useful. One can determine the pressure spike as a function of flow and volume.
The rate of change in pressure is
dp/dt = BulkModulusOfOil*Flow/VolumeOfOil
I cover this in the upcoming Hydraulics and Pneumatics.
The pressure spikes can be calculated by multiplying each side by dt and making that the update period. Because we are talking in time increments dp and dt should be thought of as Δp and Δt.
Δp = β*Flow*Δt/VolumeOfOil
β is the bulk modulus of oil which is about 160,000 psi. Flow*Δt is the same as ΔVolume
You can see the units match.
All so, you can see that if in one time period the ΔVolume changes by just 0.1% the pressure will change by 160 psi. When this is multiplied by the area, which we don't know yet, the resulting change in force can cause a shudder in the system. Therefore Δt should be kept small.
I am still waiting to hear about the existence of a counter balance valve. I am not convinced that the volume change is the whole story.