Could any one tell me how the Allen Bradley 16 input analogue card can be set up as ''class 3''? Also why is there a distinction between class 1 and class 3? The card part numbers are the same!!
Pauly
It is the one card. It is the software initialisation word you send to the card that makes it a class 1 or 3. Class 3 uses more words in your data table but does return more info. Read the manual again with this in mind. Regards Alan
AB 1746 16 NI16I
Thanks for the info, I read the manual and wondered why there would be a need to set the card up as a class 1 anyway? If there are 16 channels with 1 data and 1 status word for each channel, why would there be a needfor a class 1 setting? The use of a lower spec cpu maybe? Any info is greatly appreciated.
Thanks, Pauly
Similar Topics
Hello everyone, I'm working on a converting SLC to ControlLogix project. I have a question about 1746-NI16I card. The AI card is Class 3...
Replies
2
Views
1,789
Looking at setting up a 1746-NI16I class 3, I'm looking at the channel configuration word and have a few questions. Do I ignor bits 0,1 & 2 as...
Replies
4
Views
2,002
I have searched a bit and studied the users guide and I think I am close, but I must be missing something stupid. This is my first PLC experience...
Replies
37
Views
6,536
I've got to use a 1746-NI16I in a remote I/O chassis. Is there anywhere I can download the class 1 sample code that's shown in the user manual...
Replies
2
Views
1,708
:skuller:HELLLLO TO ALL, HERE IS THE PROBLEM I HAVE ENCLOSED A ZIPPED FILE FROM THIS APPLICATION. THE PROBLEM I AM HAVING IS THAT THE STATUS LIGHT...
Replies
6
Views
2,132
Back
Top Bottom