Ab 1756-en2t
Arunkumar G
Jul 2019
Bangalore
Hai,
When i am updating the firmware for 1756 EN2T, it got disconnected and now it is not connecting through Ethernet as well as USB.
Only OK Red led blinking, Link and Net LED are in off state
Display shows unprotected mode - change switch settings
I tried protected mode by changing 900 in switch and i rebooted again it is going to unprotected mode
I reset the device using 888 in swutch, still the error exists...
Kindly give a solution
Regards,
Arunkumar G
https://literature.rockwellautomation.com/idc/groups/literature/documents/in/1756-in603_-en-p.pdf
Page 20:
OK Red LED blinking - recoverable fault - configuration (likely because of the firmware update missing configuration)
Link - OFF - Module not ready to communicate, verify it has power
NET - Module not powered or does not have valid IP
You have a misconfigured module. You lost your config with the firmware update. The other thing is to re-seat the module in the rack. It may have a bad connection.
See page 9. Put the module in a test rack with a dummy hub/switch, set up the IP address, reconfigure the module's IP address, put back into machine.
So I have code to read the IP address of a 1756-EN2T with a MSG block - Get Single Attribute. Does anyone know where to find the MSG block...
1,144
I've been trying to get this Ethernet module configured to send emails to our relay server but cannot get it to work. the EN2T is running...
1,764
Dear All, I have been using 5561 CPU with redundancy, Few days ago, I have seen the message Disqualified on RM module of secondary PLC. and i can...
770
Good day folks, We have an L71 processor (v30.02) in a rack with an EN2T connected to the plant network & another (v10.007) used for IO only -...
2,140
I have a pair of 1756-L73 controllers on A4/A backplanes with PA72 power supplies, configured for redundant operation with RM2 and EN2T modules...
2,784