benaiahhenry - Thanks for posting a follow up with your final configuration. I have a couple suggestions for future reference.
1) On the Gate Switch SMF2 that has its inputs wired to 24V, click on Advanced Settings and disable Pulse Testing. If you leave it enabled and there is ever a cross fault (short circuit) between Test Sources MP_12 and MP_13, you will not be able to clear that fault in the Gate Switch SMF2 unless you remove that 24V signal (from BOTH channels) and then reconnect it. Normally the way you clear the fault from the SMF (after physically removing the wiring fault) is by opening and then closing the gate to turn off the inputs and then turn them on (a "Functional Test of the Input Device") - difficult when it's hard wired to 24V!
2) Consider using the "Alternative Device" SMF instead of Gate Switch for SMF2. You can configure this (in Advanced Settings) for a single NC input with pulse testing disabled - that way you only consume 1 input terminal instead of 2.
Hi Brian,
Welcome to the forum!
Thanks for the suggestions I'll keep those in mind for the next project (or if I every have to do anything to this system again)!
-Benaiah