I've been getting a weird major fault on one of our 540 E revision E processors.... S/8 watch dog timer fault... It has happened 2 days in a row. This processor has tons of I/O and memory left. Can anybody help?
Have any program changes been made recently? Watch dog timer faults activate when teh processor is unable to do everything you want in the time designated. A common cause is looping logic.
Greetings rszuszkiel ...
and welcome to the forum ... as my distinguished colleague Ken Moore has said, you should carefully check your program for excessive “looping” or “recursive” programming ...
you might also want to check the setting for the watchdog - as shown in the figure attached ...
the setting is normally entered as 500 for one-half second ... I do NOT (let me repeat that ... I do NOT) recommend just increasing the setting to “mask” the problem ... that’s sort of like just increasing the size of a fuse to keep it from blowing ...
the reason that I mention the setting is that sometimes it gets changed to a lower number by accident - or by inexperienced programmers who mistakenly think that a lower watchdog setting will somehow “speed up” their program ...
if you can’t spot the problem yourself, you’re welcome to ZIP and post your .RSP program file here ... we’ll be glad to take a look at it for you ...
(suggestion: before you post it, make sure that your employer, etc. doesn’t consider the program to be “proprietary” or contain “trade secret” information) ...
hope this helps ...
Ken & Ron :
Guess what? ... The watchdog timer setpoint was 0 mS .. I've set it to 500 to solve this problem for good..... Thanks again..
Rob
sometimes we get lucky ...
not to rain on your parade, but now the big question becomes:
HOW did it get changed? ...
if you suspect a "fat finger" on the keyboard (either yours or someone else's) then everything might be OK from here on out ... or is something in your program possibly writing a 0 to that location once in awhile? ... double-check that - and be suspicious of any HMI/SCADA type devices connected to the system ... sometimes a programmer makes a typo error to an address - and ends up with another device writing into a PLC data location over a network cable ...
cause for concern:
now you’ve got us wondering how it was running at all - with that 0 setting ...
Ron:
I have no idea who or what changed the setting to 0 .... This is a stand alone processor with ten semi automated pushbutons on it;no HMI or SCADA.(It's a new processor& rack - we're just starting to automate ) However it is on our network.. I'll keep my eye on it- Once again thanx....
Rob
Hi I have a Modicon Quantum 540 14A CPU that evertime I cycle power to it, it seems to lose the software (at least thats what the Modicon tech...
2,171
Hello, Working on a small project where I have ordered a AB 5069-L306ERS2 PLC but it's about a 4 month lead time for delivery. Going to make do...
3,401
hi, i have a machine with SAIA model number PCD2.M5540. Recently i am facing issue regarding the run and stop mode. i tried setting the plc to...
1,841
Original tl-series servo motor went bad(A2540)......replaced with newer style (TLY-A2540).Ultra 1500 throws error E.030 EEnCoP (comms not...
1,415
Has anyone had any luck with rs485 communications between a Redlion DSPLE and a Crompton 1540. I have verified unit and protocol as well as the...
1,990