AB analog card 1756-IF16 or IF8I
euro
Jul 2020
ontario
Hello,
we chose Allen-Bradley analog card 1756-IF16 for three 4-20mA current inputs for XFMR high side winding temp, low side winding temp and tank oil temp, but later i was told for different sensor inputs, IF8I should be used, since IF8I is for isolated inputs.
My question is could we still use IF16 for different inputs, i see in the manual, the connection shows it accepts several single-end inputs with RTNx jumper-ed. Is there any issue with several current inputs sharing the same point? I understand IF8I makes more sense, but not sure if IF16 is an absolutely NO for different current inputs.
Thank you
Hello,
Thank you
It wouldn't make sense to provide 16 channels on the module if only one transmitter could be connected, would it? Instruments with non-isolated outputs are rare these days, and you can mix and match different instruments with the IF16 module so long as all of them have isolated outputs. To connect an instrument with a non-isolated output, you'd need an isolation transmitter.
Thank you
what you means is as long as the sensor output is isolated each other, it is ok to connect these three sensor 4-20mA output to IF16 input, right?
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,202
Good Evening , I have a 1756-IF16 Analog Input card already installed in a working ControlLogix Rack. I need to add another Analog 4-20 ma...
2,181
Hello PLCTalk Friends, I am interested in connecting one 2-wire loop powered 4-20mA transmitter to two analog input cards. In my program, I will...
1,392
I am looking for information on the proper calibration of an 1756-IF8 analog input card, preferably the wiring of the voltage source. Rockwell...
8,028
I've got this 1756-IF8 card configured for 8 single ended inputs as shown below, but none of the channels are read real values (about 4 ma in the...
2,566