I've got a Micro850 which talks to a power meter on Modbus RTU via RS485.
I get a set of WORD data back from the power meter, each data is encoded into two words floating point number.
How do I join the 2 words into a floating point (REAL) tag in the PLC so I can use the information in the PLC?
Is there a function block where I can pack 2 words into a floating point number?
Thanks,
Normally you would specify that the data to be read is REAL and it will read two registers at the starting address you specify.
What address are you trying to read and what data type does the manual say it is?
Looking at the MSG_MODBUS function block help, it doesn't mention that you can specify REAL data types? It automatically assigns 125 WORD array to the MODBUSLOCADDR data type.
I'm trying to read address from 30001 for 60 WORD (30x REAL).
Manual of the power meter says that they are in REAL/floating point numbers.
Not familiar with the 850's on other Rockwell platforms, you could use the Copy instruction. I see the 850 has a COP block, select the first word as the input, with floating point as the output, length of 1.
Hi everyone, I would like to use Micro 850 to control DF FC 102. I adready connect Danfoss fc 102 VFD ( it can run the motor) to Micro 850 by...
1,930
All, I know this type of question has been asked (and sometimes answered) ad infinitum but after looking I'm still stuck and could use some help...
19
6,305
I am trying to read and write data from Control Logix L23E and a Micro 850. My path in the message is 2, 192.168.2.183 192.168.2.183 is the ip...
713
Hello. I have an issue with a Micro 850 PLC. Issue is when it is in RUN mode, and an output is energized, the whole PLC just turns off, then turns...
839
554