won0626 Member W Join Date Dec 2008 Location ulsan Posts 1 Dec 4, 2008 #1 Hi! i have experienced a very strange thing. When AB PLC CPU went into fault status, all digital ouputs became ON status. is there anyone experienced similar phenomenon? exact model is AB PLC5 L40E(1785 L40E) reply please..
Hi! i have experienced a very strange thing. When AB PLC CPU went into fault status, all digital ouputs became ON status. is there anyone experienced similar phenomenon? exact model is AB PLC5 L40E(1785 L40E) reply please..
boldive Member B Join Date Jul 2008 Location Toronto Posts 16 Dec 4, 2008 #2 Check settings for your outputs. Probably some of them have a flag: goes to "1" if CPU faulted.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Dec 4, 2008 #3 What is the error? Check for a fault routine. Status S:29