AB SMC Flex soft starter
Simple question replace the module
Just because the resistance checks OK it may not be turning on OK
Is there are more than one power module, try and swap there location to see if the problem moves it may tell you something.
The control boards of all SMC Flexes are exactly the same regardless of size. Inside of the power module is a chip set that tells the controller what size control module it is connected to so that the control module knows what to do and how to protect the motor. That main difference in the modules is the size of SCRs, the size of the bypass contacts, and the Hall Effect transducer used to measure current. The Hall Effect transducer is the only thing that can be read, the other components all look the same to the microprocessor. So if the HE transducer fails, or someone installs a module of the wrong size, the controller doesn't see the correct module and gives a fault. You can't change the HE on the module, the entire thing is potted.
A little more info...
60367 - Cause and Troubleshooting F38 Hall ID Fault on SMC Flex Soft Starter
Access Level: Everyone
I would zone in on Solution 2 Step 4 - "...If the resistance readings are the same, replace the SMC Flex Control Module."
Regards,
George
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
312
Hi there, very much new to AB Drives / Drives in general. Driving a pump with SMC Flex Drive Rating: Pump (5-135) Revision 6.008. Currently the...
2,162
Hi Everyone, Looking for a "Sanity Check" on my programming for Starting and Stopping a pump connected to a SMC-3 Flex Soft Starter via...
2,527
I’m not a regular user of soft starts but the SMC Flex list the aux contacts can be set to “Normal”, what does normal mean? The manual doesn't say...
5,044
I am facing a problem in which when the emergency stop is pressed, the motor comes to zero speed but going to start state instead of stop state...
1,612