AB T/C Module 1746-INT4
plcengineer
Jan 2004
USA
176
Gents,
I have a 1746-INT4 Thermocouple Module.. I have the configuration word set to 2384 and my temperatures are reading down instead of up. What could be causing this? One channel read 97 deg and then we heated up the T/C and it read 50 deg.. So, does anyone have any suggestions? Reverse wire or wrong config word..
tks,
There are many choices, page 6-2 from the user manual shows this
2384 Dec for the config gives
Type J
Eng Units x 10
Open Circuit Mode=Upscale
Degrees F
Channel ON
Giving a scaled value of -346 to 1400 F
So 2348 looks ok if the above is what you want, id try looking at polarity, wrong probe, connections, noise etc etc
I take it you have moved the config word to the module on power up (or whatever)
Module config to move 2384 to would be O:x.0 where x denotes the slot in the chassis
What are the module status LED's doing ?
In case you havent got it the user manual can be found here.
Hello, We have an older SLC500 controlled system that is using a BASIC module to communicate to a third party device. Looking into converting the...
1,282
I have been unable to make my stepper motor move. I was hoping for an example on rs500 that I could maybe look at. Or maybe some advanced help...
2,096
I have two output cards sitting next to each other in a rack: 1746-OW16 1746-OW16 (Octal) output 13 in the first card triggers a solenoid. When...
2,209
Hi, I am upgrading a AB PLc to Siemens PLC logic and everything is ready for siemens but the problem is the existing PLC is communicating to DCS...
4,779
I'll admit that in all these years I have only encountered M0/M1 files one other time, and it was used to communicate with Eurodrives. In a SLC...
1,739